how to check the insulation for motor using megger?
Answers were Sorted based on User's Feedback
Answer / omwikha
It is used to check the insulation resistance between the windings or between the windings and the earth terminal for the case of the motor. One lead of the megger is put on the earth terminal and the other lead is moved from one winding terminal to another as the megger handle is rotated for generation of voltage used for testing, the readings are noted and compared with the reference values to ascertain the condition of the motor.low values means insulation failure.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
Megger between winding terminal and the body .The voltage of
the megger should much higher than the rated voltage of the
motor.For 230and 400 V motors 500V megger is to be used.
Is This Answer Correct ? | 1 Yes | 3 No |
what is the formula for backup time of online ups?
What is a doble test
1 Answers KPSC Karnataka Public Service Corporation,
How to select the Cable size for 550 Amps Load without seeing the cable Catalogue?
what are the main applications of transistor in non-linear region?
Wat is meant by OLTC?
we change the speed of the synchronous motor by incresing or decreasing a rotor resistance
Hi all I had applied for the RRB test in the ELECRICAL category. I would be pleased if any of you can sent me previous year question papers. Please forward the question papers to varshashahi@yahoo.com Thanks and regards Varsha
please tell me formula of 3 phase induction motor under condition{1]when we 3 phase motor starts without load in star or delta connection?thanks
what is the lemen of a single 5mm 13000mcd white led pls reply
what happens if DC earthing and AC earthings are shorted?
transmission line losses
which is the best book of electrical objective for placement