what happens when ac supply is given to D.C motor.
Answers were Sorted based on User's Feedback
Answer / pandi
if A.c supply given to D.c motor more spark at brush & run
at low speed with noise
Is This Answer Correct ? | 24 Yes | 4 No |
Answer / chandan
It depends on the motor construction. If the field winding
is connected in series with the armature winding, the motor
is like a universal motor and will probably operate
normally. If the field winding is connected in parallel with
the armature, the motor will not run, but will draw current,
make noise and get hot.
Is This Answer Correct ? | 20 Yes | 0 No |
Answer / empobart jhambt baski
I want to know what is exactly the answer of this question?
Is This Answer Correct ? | 20 Yes | 3 No |
Answer / arockia doss
Its quite simple...
Motor Will run with reduce speed & With Humming noise Comes
with Steps of jerk.
Is This Answer Correct ? | 10 Yes | 1 No |
Answer / vinaykumar
it will run at very low speed and excessive heat is
produced in the motor due high hysterisis and eddy current
losses and along run may damage the motor
Is This Answer Correct ? | 10 Yes | 2 No |
Answer / pradeep kumar rawat
When ac supply is ginen to DC motor, DC motor will run with
less speed and prodeced some noice.
Is This Answer Correct ? | 24 Yes | 18 No |
Answer / mr.anant ram yadav
if A.c. supply given to D.c. motor the net torqe will be
zero and motor will not work. bez postive &negative cycle
is zero.
Is This Answer Correct ? | 19 Yes | 14 No |
Answer / manish
dc motor does no work on ac.it will not rotate because in
india ac frequency is 50 hz so the time of half cycle is
only 10 ms.this time is too short to move because of its
inertia.
but expeptionaly dc series motor will rotate when it is
given to ac supply.
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / swarupa
In ac supply the magnitude and direction of voltage or
current changes for every half cycles so the dc motor may run
but in very low speed due to less torque develop & also due
to inertia.If it is run continue the frequency losses may
increase due to high heat.The efficiency poor.
Is This Answer Correct ? | 2 Yes | 0 No |
why we have to particulary use ACB for below ratings,even available of MCB,MCCB with that range ?
Dear Friends, Need your help for connecting APFC panel, Quotation : I have 2 No’s 1000 KVA Transformers, both transformers are having separate APFC panels, ( Tr-1,400KVAR, TR-2,450 KVAR) Now I want to stop One transformer, present load is 650Amps, Max, So One transformer is enough, I have switched OFF TR-1, but PF is not maintaining properly, its 0.5, So now I want to connect TR-2 APFC also in TR-1 Loads, Can any one answer for my Quotation with drawing, how to connect TR-2 APFC panel in TR-1 Loads,
1.wat is the purpose (or)function of regulator? 2.wat is the purpose of stabiliser?
during positive and negative half cycle of ac supply what happenes in the load?
We have one 500KVA transformer. We have tested REF relay and commissioned. After one and half year, due to some ground fault in one of the DB circuit Transformer tripped by REF relay. What will be cause and remedy. Please advise?
what is neutral ground resistance relay? how it is helpful in protecting system?
What are locations arc protection relay is fixed.
How to calculate the input cable rating for 10kva ups (3phase input and single phase output and also 3phase output, battery rating 65Ah)provide the formula also.thnx
why transformer are not used in D.C SUPPLY
How does the sensitive earth fault protection provided by cbct for motor can help in reducing the size of cable used to supply the motor?
What is the function of retrip in busbar?
what we happen if 400 kvar cpacitor banks are on in manual mode and there is no load on mains ??????????????