what is ferranti effect?
Answers were Sorted based on User's Feedback
Answer / venkatesh
output voltage is greater than the input voltage or
receiveing end voltage is greater than the sending end
voltage
| Is This Answer Correct ? | 26 Yes | 2 No |
Answer / mahesh sali
ferranti effect is mostly occur on EHV transmission line ,
Ferranti effect is effect where receiving end voltage is
greater than sending end voltage, this is happened because
of following reason ;
1) Due to the line charging capacitor voltage between the
line and ground , adding some voltage into the line , that
will cause to get higher voltage at receiving end.
2) At load light load condition , compensation devices at
receiving end for voltage compensation adding the voltage
into the system , that will cause to get the higher
voltage
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / ahmed
This effect normally occurs when cables are used as tranmission medium...it's because in cables, the capacitive reactance is normally greater then the inductive reactance resulting in the rise of receiving end voltage to a level greater then the sending end.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / arunkutti
it s simply explained.SENDING END VOLTAGE<RECEVING END
VOLTAGE.BASICALLY is not possible .but some times occrs in
surge impedence
| Is This Answer Correct ? | 6 Yes | 2 No |
Answer / pasha
Ferranti effect is when the capacitive quality of line
exceeds the inductive capability causing a higher end
voltage compared to the voltage at the start of the line.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / nagarjuna
WHEN THE INPUT VOLTAGE IS LOWER THAN THE OUTPUT VOLTAGE ,THEN WE SAY THAT IT IS FERRANTI EFFECT.THIS WIL OCCUR DUE TO HIGHER CAPACITANCE IN LINE THAN INDUCTANCE.
| Is This Answer Correct ? | 6 Yes | 2 No |
Answer / lipunkumar2011@gmail.com
Ferranti effect is occurred in medium and long transmission line. The receiving end voltage is greater than sending end voltage at no load or light load due to capacitance effect.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / maharaja.a
THE SENDING END VOLTAGE IS LESSER THAN RECEVING END VOLTAGE
| Is This Answer Correct ? | 3 Yes | 4 No |
Comparision of Air break circuit breaker, SF6 Circuit breaker and vacuum circuit breaker.
what will happen if secondary of potential transformer (220kv/110volt) of any metering core or protection core (cables) of any phase got earthed??
how to select cable size according to ampere.
what is IP55,IP65
What are root loci?
What is the difference between amorphous core transformer and CRGO core transformer?.
This is reqd for a 1MW Solar power plant..We have 2DC outputs from the solar panels Connected to 2INVERTOR panels.. Output from invertor is 3ph,280v,500kva,50hz.These are connected to individual ACB.This has to be stepped up to 11KV ,1250KVA SYSTEM.Now can I use (1) one more ACBTO GIVE A COMBINED OUTPUT OF 1000KVA,280V & STEP UP THE OUTPUT BY USING a single two winding 3 ph transformer 11kv/1250kva. or (2)use the two outputs and connect to one three winding transformer of above rating..Pls suggestwith details.
what is the full form of ka (100A mccb KA)
how can i get the formula to find out the cable size if i know the load of main fuse protection.
what is vA rating and class of a ct.
why capacitor using the induction motor?
what happen when transformer connect on dc supply.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)