Answer / pradyumna chandra panda
For 11kv suppy it is 40kv/2mm at normal temprature is ok. As per my experience it is reach upto 125kv/2mm at 40°c after filtration but we keep it 60kv/2mm NB-Below 24kv/2mm is rejected oil.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / koti
As per IS : 335-1993, it is 30 KV(unfiltered)
and 60 KV(After filtration).
| Is This Answer Correct ? | 2 Yes | 0 No |
Please let me know when replacing electromechanical Relays for protection of generators with sr489 multilin Relay, then there is no need to use 86 master trip relay Too. I am wondering this multilin relay has no contact to Stop breaker reclosing as 86 does
campared to ac, in dc corona loss is
What is the correct procedure to shutdown VCB in 11kv substation.safety and work procedure
Why should we use the igniter in the sodium vapour lamp.
7 Answers ABB, Delphi, Mudhra, NTPC, PICT,
why transformer rating is always in KVA
how we are desining 63.5 ohm resistor for NGR of alternator?
what is resticted earth fault protection ? how did it protect & work in power transformer
How to design the earth grid for lightning protection in an industry
What is current chopping in CB?
What must be the distance between the Earth pit which are grounded from two different sources. Example: Distance between the earth pit for LV Panel-1 & 2
What is the SPEED of electricity?
State norton’s theorem?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)