What should be the BDV value of a new transformer oil
Answers were Sorted based on User's Feedback
Answer / pradyumna chandra panda
For 11kv suppy it is 40kv/2mm at normal temprature is ok. As per my experience it is reach upto 125kv/2mm at 40°c after filtration but we keep it 60kv/2mm NB-Below 24kv/2mm is rejected oil.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / koti
As per IS : 335-1993, it is 30 KV(unfiltered)
and 60 KV(After filtration).
| Is This Answer Correct ? | 2 Yes | 0 No |
How earthing/grounding done in aeroplanes and ships.
how to select energy meter? have any calculation?
Why Lighting transformers are used? what will be the current if lightings connected through direct raw power?
what is difference between 5A and 100A CT constructional wise and operation?
what is distribution board?
What is meant by stator? What is meant by rotor?
Why stand-by earth fault relay and restricted earth fault relays are connected between neutral and ground in transformer?
how much kn lightning arrestor is used in 11kv line
the minimum clearance b/w ceiling and plane of leaf of ceilng fan shall be ..........mm
Why the transformers are rated in KVA ? in new view
how can we charged the battery in DG
What is the role of feedback in a closed loop control system?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)