In a Circuit how the MCB and Fuse ratings are calculated.
And shall the fuse follws the MCB or it is otherwise?
Answers were Sorted based on User's Feedback
Answer / sanjay kumar
FUSE RATING CAN BE CALCULATED AS FOLLOWS:
SAY A MOTOR FULL LOAD CURRENT RATING IS 30A,TAKE FUSE OF
RATING 2.5TIMES OF FLC. SO FUSE RATING WILL BE 80A.IF IN
CASE THIS RATING FUSE IS NOT AVAILABLE, WE CAN GO FOR NEXT
HIGHER LEVEL. BUT IF NEXT HIGHER LEVEL FUSE IS SO HIGH THAT
IT CANT BE TAKE THEN GO FOR SOMEWHAT LOWER LEVEL. THIS IS
BASED ON MY EXPERIENCE IN THE INDUSTRY.
SECOND PAART IS FOR MCB:
MCB SELECTION SHOULD BE SOMEWHAT HIGHER THAN FUSE RATING.
| Is This Answer Correct ? | 5 Yes | 4 No |
Answer / amaravathi
fuse rating will be calculated by following formula.
125% of rated current.but we can use nearest value of fuse rating value.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / devamanohar
The MCB rating shall be more than the fuse rating if it is
used for the service to switch off & on while the circuit
is in service.The fuse rating shall be 200% of the rated
curent normally as it is used for short circuit
protection.If the MCB is stay put type(No operation while
in service) it can be selected for rated current or 1.2
times of rated current value.
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / shaik
depending on the full load capacity ratings is calculated.
It is not necessary to connect MCB and fuse both,one is
enough.if u want to connect both then first fuse the MCB
| Is This Answer Correct ? | 11 Yes | 15 No |
Answer / mahesh s.chorghe
MCB RATING SHOULD BE 2.5 TIMES OF LOAD CURRENT AND FUSE
RATING GRETER THAN (1.5 TIMES)MCB
| Is This Answer Correct ? | 14 Yes | 29 No |
Answer / moideen.t.y
Fuse size can be calculated by this formula, 225% of full
load current.
locked rotor amps is the 500% of full load current.
| Is This Answer Correct ? | 4 Yes | 19 No |
Please explain open transition and closed transistion system in Star delta Starter?and also the state difference of both?
What is value of earth resistance required for substation and equipment earthing and what are the reference guidelines
is it possible to convert electrical energy to light energy for transmission purposes?
What will happen to the speed of synchronous machine subjected beyond the pull out torque? Are the behavior shown by rotor remains same for both the alternator and motor?
What is the basic difference between the electrical engineering and electronic engineering?
where we take earth in hill station
What is ERD used in Elevators??
what is the different between DC & AC load Line.
sir, why alternator output is connected to delta side in to generating transformer? any reasion?
What is the full form of CNC in electrical mechines.......?
what happens when a power transformer neutral earthing broken???
how to stop oil leakage in power transformer.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)