Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


In a Circuit how the MCB and Fuse ratings are calculated.
And shall the fuse follws the MCB or it is otherwise?

Answers were Sorted based on User's Feedback



In a Circuit how the MCB and Fuse ratings are calculated. And shall the fuse follws the MCB or it ..

Answer / sanjay kumar

FUSE RATING CAN BE CALCULATED AS FOLLOWS:
SAY A MOTOR FULL LOAD CURRENT RATING IS 30A,TAKE FUSE OF
RATING 2.5TIMES OF FLC. SO FUSE RATING WILL BE 80A.IF IN
CASE THIS RATING FUSE IS NOT AVAILABLE, WE CAN GO FOR NEXT
HIGHER LEVEL. BUT IF NEXT HIGHER LEVEL FUSE IS SO HIGH THAT
IT CANT BE TAKE THEN GO FOR SOMEWHAT LOWER LEVEL. THIS IS
BASED ON MY EXPERIENCE IN THE INDUSTRY.


SECOND PAART IS FOR MCB:

MCB SELECTION SHOULD BE SOMEWHAT HIGHER THAN FUSE RATING.

Is This Answer Correct ?    5 Yes 4 No

In a Circuit how the MCB and Fuse ratings are calculated. And shall the fuse follws the MCB or it ..

Answer / amaravathi

fuse rating will be calculated by following formula.
125% of rated current.but we can use nearest value of fuse rating value.

Is This Answer Correct ?    1 Yes 0 No

In a Circuit how the MCB and Fuse ratings are calculated. And shall the fuse follws the MCB or it ..

Answer / devamanohar

The MCB rating shall be more than the fuse rating if it is
used for the service to switch off & on while the circuit
is in service.The fuse rating shall be 200% of the rated
curent normally as it is used for short circuit
protection.If the MCB is stay put type(No operation while
in service) it can be selected for rated current or 1.2
times of rated current value.

Is This Answer Correct ?    2 Yes 2 No

In a Circuit how the MCB and Fuse ratings are calculated. And shall the fuse follws the MCB or it ..

Answer / shaik

depending on the full load capacity ratings is calculated.
It is not necessary to connect MCB and fuse both,one is
enough.if u want to connect both then first fuse the MCB

Is This Answer Correct ?    11 Yes 15 No

In a Circuit how the MCB and Fuse ratings are calculated. And shall the fuse follws the MCB or it ..

Answer / mahesh s.chorghe

MCB RATING SHOULD BE 2.5 TIMES OF LOAD CURRENT AND FUSE
RATING GRETER THAN (1.5 TIMES)MCB

Is This Answer Correct ?    14 Yes 29 No

In a Circuit how the MCB and Fuse ratings are calculated. And shall the fuse follws the MCB or it ..

Answer / moideen.t.y

Fuse size can be calculated by this formula, 225% of full
load current.
locked rotor amps is the 500% of full load current.

Is This Answer Correct ?    4 Yes 19 No

Post New Answer

More Electrical Engineering Interview Questions

what is the difference between diode and zener diode?

21 Answers  


can u give me a brief idea about power line carrier communication ??

0 Answers  


What is the impact of MCCB & MPCB on Distributed Control System?

6 Answers  


Which device of PlC does share load between DG sets when DG are running in perallel?

0 Answers  


Transformer Specification say 66/11KV, 23/27/35MVA OFDAN,what is OFDAN? we know ONAN,ONAF or OFAF

2 Answers   Siemens,


why the rating of transformer in k.v.a

4 Answers  


how does a liquid starter reduce the starting currents?

0 Answers  


What happens if there is no nuetral in the power system?

5 Answers  


Ac generato how produce power I need for camplet defination

0 Answers   KCL,


What should be value of Circuit breaker operating time and tripping time?

3 Answers  


Why Transformer does not work in DC ?

5 Answers  


last week we did the REF relay test by closing single pole (R phase) of CB and apply 380V at the primary of delta transformer. we get 33A at the primary of the R phase star end. but we get 380A at both R an B in delta side. how and why?

1 Answers   Siemens,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)