Why earthing transformer used in Distribution Sub-Station?
Answers were Sorted based on User's Feedback
Hi questioner,
Earthing T/F or T/Fs are not required in distubution S/S.
For example, here in Nigeria the distribution volage for
the T/F is either 11/0.415kV or 33/0.415kV detla-star.
However, in Transmission S/S where there are 132/33kV star-
delta connected T/F or T/Fs earthing T/F or T/Fs are
necessary. The earthing T/F is connected on the 33kV side
of the main T/F while the star-point of earhing T/F is
connected to ground to provide an artificial star-point for
the main T/F. This so because 33kV distribution ground-
fault current must flow back to the main T/F. Earth fault
protection for the main T/F must sense this current and
isolate the main T/F otherwise the earthing T/F will roast
i.e. burn.
| Is This Answer Correct ? | 12 Yes | 3 No |
Further to my answer,note that a ground fault at the
distribution S/S must be sensed fast by the relay so as to
trip the disribution cb before the cb for the 132/33kV in
the Transmission S/S is trip by its relay as a back-up.
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / deep
in delta connected t/f winding has not neutral point to connect to ground and beacuse LG,LLG fault is sensed by zero sequence current so providing earting on delta side we use earthing t/f.
| Is This Answer Correct ? | 0 Yes | 0 No |
why we not used 11kva as a direct our electrnics component.
wat is power factor
a 230v transformer with step down ratio 19:1.it has 2000turns on primary and rated 25va calculate max primary current no of secondary turns volts/turn
If the primary side current of 33/11 transformer is 64 amps then what will be secondary side current?
what is reluctance?
why white color LED light is not possible?
An 11kv system consisting of an underground cable to a sub station about 300 meters away was shut down for about 10 hrs. On energising, it tripped off on earth fault about 10---20 mins later 6 times but since than it is not tripping.its already 3 weeks now. The SPAJ was found to be fine. what could be the cause.No test had been done to determine the cause of the trippings till now because of demand.
why the transformer primary and secondary windins vector groups vary? why it is something like Dy11 and not as Dy or Yy...
what is the difference between Power and Distribution transformers ?
what are the differance between neutral and earthing?
what is meant by directional earth fault and non directional earth fault? describe both.
What will be the minimum megger value of 1700 KVA Transformer? a) Do megger value varies according to climate conditions and area . b) If megger value is 100 mega ohm is it good for new transfomer. Explain?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)