Answer / kapil mishra
floating earthing means the neutral is not earth by any
means like solid earthing ,or impedence earthing etc. due
to that if any earth fault occur in any phase the other
phase voltage increase root 3 times from the earth but
faulty phase voltage become zero from the earth. but your
line voltage remain the same.
| Is This Answer Correct ? | 19 Yes | 3 No |
Answer / ashish
Floating Neutral Means Neautral is Not Grounded & If there
is Any earth Fault Occured On Any One Phase As A Result Of
that The Voltage Of Other Two Phase Will Be Equal to line
Voltage.
| Is This Answer Correct ? | 14 Yes | 6 No |
Answer / ankur
The supply neutral point is eathed by a solid link by the
electic supply company.Hence neutral voltage w.r.t earth is
abut 2 to 3 volts. When the neutral link or neutral wire of
supply company breaks, the neutral point starts folating.
depending upon unbalance of the load on three phases, the
voltage on each phase fluctuates from as high as 350-400V to
as low as 50-100V. As a result of tis voltage apears
fluctuating & lights flicker.It normally results in damage
of power supply in various appliances like T.V.& also
damages motors in fans, mixers, fridge etc. of many
consumers in a building.
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / ashish
floting neutral means due to if voltage in all three phase
is not same due to asymmetrical load at output then voltage
drop through all phase are not same so neutral point is
shifted from center is prevent by mainten constant load at
all phase
| Is This Answer Correct ? | 20 Yes | 14 No |
Answer / manoj
floting neutral is one whose voltage is not constant.
it is prevented by use of NGR
| Is This Answer Correct ? | 15 Yes | 22 No |
Answer / sonali
floating neutral means NO neutral wire connection.
| Is This Answer Correct ? | 1 Yes | 18 No |
how to prepare the technical test
dear sir, How i calculate the 2 phase welding transformer power or kva?? kindly tell me....
what is d check in dg 1500kva
Zone of protection and tripping scheme of arc protection relay.
What is the value of system voltage?
what is inverter
what is rated voltage?
checking procedure of capacitor based motors.used in fans etc?
what is black out?,what is brown out?
power inverter we are using 2n3773 power transister in that places we can use any IGBT ?
We have two Al.busbars each of size 125mm*10 mm connected in parallel.To increase the current rating ,can we connect third busbar of size 100mm*10mm in parallel to existing two busbars?In my opinion ,if we connect busbars of different sizes in parallel,then the busbar of lowest size will take much current.So this type of paralleling should be avoided .Am I correct?
How does "OUT OF STEP" relay ,for Synchronous motor protection, work?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)