Answer / sreenu
Based on KW/HP value the current rating can be caluculated
and based on current rating of Mains & cable size can be
caluculated.
for example.
HP of the motor is :A HP
KW of load is :A HP/735.5*Efficiency(E).
Generally eddicieny of the motor can be asuumed 0.8 to 0.9
Current(C) is :A HP/735.5*E*(1.73*V* cosQ)
Cos Q generally asumed as 0.8 to 0.9
If the value of current is C, the current capacity of cable
reuired is Appx. 1.5*C.
Based on cable catalogue provided by the cable manufacturer
the size of the cable can be selected.
For eample. If you use al. cable, the size of cable is
bigger than copper cable.
Rating of mains: 1.5* C, but fuse arting is C only.
Is This Answer Correct ? | 3 Yes | 1 No |
Whats meant by trivector meter where it is connected at the substation?
20 Answers GPIL, Infosys, Jakson, L&T, Secure Meters,
What is the universal motor?
what is power load and lighiting load?
Why dont we get shock while testing for voltage with a line tester? How the bulb inside the tester glows while testing with tester coz we are totaly isolated from earth or we are not giving close path for the current to flow?
what is the IPC ? & what the uses ?
what is an alternator & generator
374kvar capacitor bank connected across 600kw,6.6kv motor.what will happen if motor run at 50% , whether full kvar applied or half?
why stone used in Transformer yard.
what is reactive power and active power
IN a transformer during power supply how the LV and HV bushing works??
What is dry and wet flashover.
A dc motor running on dc drive whose input is 3ph AC what will happen if we change the phase sequence of dc drive for e.g (R Y B) is connect as R B Y, will the motor run as same as previously running before changing phase without any effect