Answer / prasad
Star or Delta are types of winding connections for 3 phase
systems. The line current is the current passing thru
conductor to these windings. The ammeter is generally used
to measure current thru those conductors & not winding.
This current is known as line current. While the current
passing thru each phase of winding is known as phase
current.
In Star winding entire line current passes thru
individual phase i.e. I(ph)=I(L)
In Delta winding however line current gets divided in two
windings. Here I(ph)=I(L)/1.732. Here 1.732 is square root
of 3.
| Is This Answer Correct ? | 214 Yes | 35 No |
Answer / mani
The phase current is current flow between phase to neutral
is called phase current and the line current is current
flow between two phases is called line current.
In Star winding entire line current passes thru
individual phase i.e. I(ph)=I(L)
In Delta winding however line current gets divided in two
windings. Here I(ph)=I(L)/1.732. Here 1.732 is square root
of 3.
| Is This Answer Correct ? | 138 Yes | 39 No |
Answer / gagan kumar gupta
in star system line current will equal to phase current and
delta system occured line current will equal 1.732*phase
current
| Is This Answer Correct ? | 29 Yes | 10 No |
Answer / kupstar tange
Line current is the current that is flowing from an AC supply and Phase current is the current that is flowing through each phase in the system.
In a star system the line current is equal to the phase current (IL = IP)
in a delta system, the line current is divided by 1.732 to get the phase current ( IP = IL/1.732)
| Is This Answer Correct ? | 18 Yes | 8 No |
Answer / mandeep
In a 3-phase system current accross any one phase and
neutral is called phase current whereas current accross any
two phases is called phase current.In star connection phase
currrent = line current wheras in delta connection line
current = 1.732 phase current.
| Is This Answer Correct ? | 13 Yes | 13 No |
Answer / rajeev kr. roy
in 3 phase system star and delta connection r used
according 2 requirement.now,phase current is d current
between any phase,line current is d current betwen one
phase and neutral line. in y-y connection line
current=phase current,in delta connections line
current=1.732 times of phase current.
| Is This Answer Correct ? | 15 Yes | 25 No |
Answer / asjad iqbal
in there phase supply mean star delta .no ny diffrance
between line curent and phase curent.
| Is This Answer Correct ? | 9 Yes | 54 No |
Answer / deepak ranu sharma
IN STAR CONNECTIONS THERE IS A NEUTRAL POINT SO PHASE
CURRENT IS 1.732 TIMES OF LINE CURRENT AND LINE CURRENT IS
THAT CURRENT WHICH IS PASSING THROUGH A LOAD THROUGH PHASE
AND NEUTRAL.
IN DELTA CONNECTIONS THERE IS NO NEUTRAL SO THE LINE
CURRENT IS SAME AS PHASE CURRENT.
| Is This Answer Correct ? | 6 Yes | 56 No |
Answer / deepak ranu sharma
IN THE SYSTEM OF 3 PHASE STAR CONNECTIONS THERE IS A
NEUTRAL POINT SO THE PHASE CURRENT IS 1.732 TIMES MORE THAN
LINE CURRENT.AND IN DELTA CONNECTIONS LINE CURRENT IS EQUAL
TO PHASE CURRENT.
| Is This Answer Correct ? | 12 Yes | 83 No |
To make a basic instrumentation amplifier, it takes A One op-amp with a certain feedback arrangement B Two op-amp and seven resistors C Three op-amps and seven capacitors D Three op-amps and seven resistors
how to calculate H.P of a moter from speed of a moter?
High voltage test procedure of in swgr board. why should measure millivolt drop on testing time?
What is 2P*0.5 sqmm screened copper cable and what is the use of it..?
explain the meaning of harmonic resonance
2.5mva transformer is installed in our company with oltc but it is not working in auto mode ,it is operative in manual mode control wiring is done how can i rectify it?
what is the minimum clearance between a 11KV 150KVAR capacitor cell and series reactor.can a series reactor can be mounted in the same structure of the capacitor cells structure
difference between local breaker backup relay or backup protection relay ?
what is the formula of knowing the clabe size on any load?
In transmission line 11kv,33kv etc are rms values are peak or others??
What is the Ideal Earth to Neutral Rating for Techonology Equipment like Routers, Switched, PABX, Computers etc etc?
What is the purpose of SOTF being used inspite of distance Protection given?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)