What is the use of 1:1 isolation t/f in any circuit...?
Answers were Sorted based on User's Feedback
Answer / aamod tripathi.
The main use of Isolation Transformer is to Isolate the
circuit without changing the voltage ratio. i.e. 1:1. It is
generally used in LT (415 V Three phase systems).
The isolation is needed because the LT system is much prone
to faults and the faults like line to ground faults are
common. At this level of voltage most of the petty but
important loads are connected. Human interface is maximum
and the system is not as Ingress protected as in case of HT
switchgear (Where seperate room and skilled persons only
have access). Therefore the fault level is dangerous and the
consequences can be even dangerous. Therefore to Reduce
fault level Firstly a transformer is inserted thus its
impedance %z comes into circuit (Series Impedance). And even
if fault occours you/ Device is isolated from the main
circuit which is actually feeding the fault. Thus it keeps
one safe and Protects severe damages that could have
happened otherwise.
| Is This Answer Correct ? | 10 Yes | 0 No |
Answer / bala
simply saying isolation of any circuit is used to isolate
from line to line line to ground and also for human shock
resist, because everyone did not know about the risk and
dangerous of electricity only skilled will know about it. so
every circuit is should be isolated for safer use
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / n k singh
The main use of isolation transformer is to isolate two
electrical circuits.
| Is This Answer Correct ? | 0 Yes | 0 No |
hwat type of motor is used in thermal gas turbine hydro nuclear power plants and why
A jet of fluid strikes a plate What was the force required to counter it?
What makes the difference between 50Hz supply and 60Hz supply which one is economical? What is the use of using increased frequency?
there is a power transformer 66/11kV in delta-delta connection has 5 feeder coming out from the secondary side. One of the feeder in it normally loaded (loaded than other feeder)and this feeder usually trips with double OCR causing the bank transformer to trip. Now if the load of this feeder is put on other transformer then that no problems occurs on that transformer or the load. However normally all the test(IR, PI, short ckt, open ckt,grounding test and other ) has been conducted for this but evertything transformer..... I am not geting what is the actual problem...
How to Calculate the maximum Demand required for a connected load for a manufacturing Plant
Why current leads the voltage in case of capacitor load? Why voltage leads the current in case of inductive load? Why both are with in phase in case of restive load?
why 3 phase is converted into 2 phase using electronics circuit why not 2 phases are diresctly putted from the 3 phase transformer??
what is voltage gradient?
My meter CT is 200/5amps Then my electrical meter MF=???please suggest
what is earth pit , how we can measured it, what earth rods reference
in thermal power plant the steam produced is made to cool after falling on the turbine blades. my question is why this is done while the same is needed to heat up again. "jab pani ko wapis garam hi karna hai to thanda kyu karte hai"
how to select proper cable for ct wiring so that drop within the limit.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)