Answer / suman chakraborty
First you need to check the excitation voltage which is feed from the controller part then see the mile volt from the load cell side,Then according to the change the load if the voltage changes then primarily the load cell is okay.
| Is This Answer Correct ? | 11 Yes | 3 No |
Answer / maheshrp
Physically load cell two wire supply and two wire output,so output wire side check resistance that 0.350k it's ok after bad loadcell check resistance 0.450k this is bad
All load cell Wright capacity on load cell
| Is This Answer Correct ? | 1 Yes | 0 No |
To become an Instrument DESIGN engineer, is there any softwares or training to become Instrument Design engineer, plz suggest me, Iam very much interested in designing.
what is loop folder?
1 Answers Bapco Bahrain Petroleum Company, Hyundai,
what does mean by analog output trim and where this one used for?
What is cable size for intrenal wiring in DCS or PLC ,from any card to Terminal amd Why
Sir, I am working as a Instrument Engineer in Grasim Industries. Can any body provide question answer for interview purpose
For a diafhram 1.5 d =kn(p-p0) D4 Where d in deflection in inch k=constant n=no of capdule (P-P0)=Applied pressure in psi D In active dia at capsule. -1.5 d=k to p d being constant -1.5
0 Answers L&T, Shiv Tech Marine Control,
If a differential pressure transmitter is calibrated for 0~2500 mmH2o and transmits a 4~20mA dc signal. The transmitter is placed across an orifice plate which is sized to create 2500 mmH2o differential at 5000m3/Hr a) what is the flow rate when the transmitter signal is 13.0mA DC? b) what is the signal output of the transmitter when flow rate is 2500 m3/Hr ?
Can we get the outpot in c without using getch fiction? Answer is yes but output will stay on display 4 only few second.... But can we get output without using getch and also output will hold on the display...?
what is sequence table in DCS . make a logic in sequence table for tripping of ID fan in Boiler(in YOKOGAWA CS 3000 DCS).
What is electronics?
What is the IEC Standard for PLC I/O Terminal wiring Procedure?
i have steam drum height 1000mm. and i want to placed the transmitter below the tap.how i calculate.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)