Why do we go for 4-20mA? why not other standara?
Answers were Sorted based on User's Feedback
In long distance wire if some wire are broken then at the
receiver end there will be current value 0. If we take 0-20
standard in that case it will be difficult to know that the
current value is actually 0 or its 0 because of broken wire.
but in case of 4-20 it the the signal is in off state then
at the receiver end we will have current value 4 and in
case of broken wore we will have current value 0.
| Is This Answer Correct ? | 17 Yes | 2 No |
Answer / bhanu prabhath
yes, i agree with JB,s answar, to some exctent, some times transmitter 0 drifts due to calibration disterbance,if we use 0-20ma we cont find the -ve 0 drift of the transmitter in case of 4-20 the drift will be within the 0-4ma. also the 4-20ma is easy to equal division and calculate with any range .
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / parag pathak
Signal can be sent via voltage, but as signal will be drop
if it has to sent long distance,but current signal will not
not lost,so we are preffering current signal over voltage
signal. secondly we can use 0-20 mA instead of 4-20 mA, but
then we cannot know whether it is dead zero or 0 reading.
Now once any manufacturer make any standard it is accepted
throughout so that new Instrument will also be compatible
with that system.
| Is This Answer Correct ? | 2 Yes | 0 No |
We are using 4 -20 ma because we will get linear current
with respect to 24 V,so i most of cases 4-20ma is used.
If u want to try plese plot a graph and check.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / muthu
in communication, some loss occurs . if we sent 0-20 mA
signal through comunication, 0-4 mA vanishes due to loss.
so 4-20 mA current signal are preferred in standard.
| Is This Answer Correct ? | 3 Yes | 5 No |
Answer / anwar azim
Other communication methods suppose RS232 are having
constrains for long distance communication and require
repeater after some distance and are prone to external
disturbances.4-20mA is not prone to external disturbances
and the cabling can be done for long distances with out any
effect on signal.
| Is This Answer Correct ? | 1 Yes | 10 No |
I want to measure flow by using DP Tx and range is 0 to 1200 Kg/cm2 ?
What is the difference between pt100, pt500 and pt1000 RTDs?
what is differance between SOE an alarams
Waht is surge in compressors and how to control it?
How can you convert an SR Flip-flop to a JK Flip-flop?
WHAT IS TSI? HOW ITS WORK
why the output sugnal is 4-20 ma and not 4-25 ma?
how u calibrate sox nox co2 co in cemps?what is opacity n HPm?tell the standard parameters of cems?
How we can re-range the DP transmitter, range is -0.5 to 2.0bara. new range is -0.5 to 5 bar
what is meant by nuclear power plant?
what is a instrumentation ?
generally transmitter power supply having some range(12v to 35v) but the out put(4-20 mA) must same for given input.If we vary the power supply voltage then output mA also to be change according to V=IR. Is there any voltage regulator in the transmitter ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)