Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


What's the difference between cold loop test and hot loop test?

Answers were Sorted based on User's Feedback



What's the difference between cold loop test and hot loop test?..

Answer / ravi

1.Cold Loop Check 
This is an electrical continuity check to confirm wiring integrity from control panel's terminal block to the field instrument. Please note that field cabling starts from field instrument and goes through Junction boxes and marshaling cubicle to reach termianal blocks of the control panel 




2.Hot loop check 
After successful cold loop check, each I/O is subjected to hot loop check. In this testing entire loop functionality is checked by simulation of the signal with power up from DCS or PLC 
1.Calibration range 
2.Activation of inputs / outputs / Field switches / Solenoids 
3.PLC/DCS register updates 
4.SCADA updates

Is This Answer Correct ?    102 Yes 2 No

What's the difference between cold loop test and hot loop test?..

Answer / jain

Cold loop check may also called as continuity test, to identify weather the cable are terminated at its correct terminal blocks from field side instruments to Control panel. At this time no power is present in the loop, or it may be isolated from the power source. It can be done using a Multi meter.

Hot loop check is done after cold loop test to identify the instrument is at correct range, units, and its dependency with the control instrument. so can be change and calibrate using a communicator or manually while the instrument is energized from the panel by 24 volt or vice versa.

Is This Answer Correct ?    11 Yes 0 No

What's the difference between cold loop test and hot loop test?..

Answer / hasan

Cold loop checking = continuity test, ir test make sure the cables are damaged or un damaged

Hot loop checking = instrument functionality test its means the instrument is in running condition if any fault may occur r not its should be make sure

Is This Answer Correct ?    5 Yes 0 No

What's the difference between cold loop test and hot loop test?..

Answer / ajinkya

I think...
Cold loop test is done using simulator
Hot loop test is done actually in field

Is This Answer Correct ?    6 Yes 63 No

What's the difference between cold loop test and hot loop test?..

Answer / jaydip khatri

hot loop mean instrument to J.B. & cold loop mean J.B. to panal.

Is This Answer Correct ?    5 Yes 73 No

Post New Answer

More Instrumentation Interview Questions

Technician A says the brake warning light is connected into both the parking and service brake systems. Technician B says the brake warning light will come ON only if the service brake system fails. Who is correct?

2 Answers  


what will be the output of a temperature transmitter if temperature is 120 degree celcius?

6 Answers   KNPC,


1.can you use SCADA instead of DCS,DCS instead SCADA 2.Difference between DCS and PLC,can their role be reversed i.e. role interchange 3.Difference between RTU and PLC

0 Answers   IOCL, Lakshmi Machine Works,


how many maximum enter 2mm Dia solid cylindrical pipe into 8mm Dia hollow cylindrical pipe. give answer with calculation.

0 Answers  


If a flow transmitter (magnetic type FT) that can measure flow and temperature, then why in some industries people use flow transmitter and temperature transmitter in the same line 1 after another? Even after 1 single flow FT is capable of measuring flow as well as temperature.

1 Answers   Process Control Technologies,


how to work gas chromatography explain principle ?

2 Answers  


How to calculate mmwc values into tonnes?

0 Answers  


what happen if i install my pressure transmitter below the elevation of pipe in natural gas service. Also support your answer

3 Answers   C2C,


Flame scanner

1 Answers  


HOW CAN I CONNECT ROSEMOUNT 3300 LEVEL TRANSMITTER TO Allen-Bradley SLC500

1 Answers  


define feed forward control loop with example and drawing?

0 Answers   Honeywell,


I need circuit for RTD senser?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)