What's the difference between cold loop test and hot loop test?
Answers were Sorted based on User's Feedback
Answer / ravi
1.Cold Loop Check
This is an electrical continuity check to confirm wiring integrity from control panel's terminal block to the field instrument. Please note that field cabling starts from field instrument and goes through Junction boxes and marshaling cubicle to reach termianal blocks of the control panel
2.Hot loop check
After successful cold loop check, each I/O is subjected to hot loop check. In this testing entire loop functionality is checked by simulation of the signal with power up from DCS or PLC
1.Calibration range
2.Activation of inputs / outputs / Field switches / Solenoids
3.PLC/DCS register updates
4.SCADA updates
| Is This Answer Correct ? | 102 Yes | 2 No |
Answer / jain
Cold loop check may also called as continuity test, to identify weather the cable are terminated at its correct terminal blocks from field side instruments to Control panel. At this time no power is present in the loop, or it may be isolated from the power source. It can be done using a Multi meter.
Hot loop check is done after cold loop test to identify the instrument is at correct range, units, and its dependency with the control instrument. so can be change and calibrate using a communicator or manually while the instrument is energized from the panel by 24 volt or vice versa.
| Is This Answer Correct ? | 11 Yes | 0 No |
Answer / hasan
Cold loop checking = continuity test, ir test make sure the cables are damaged or un damaged
Hot loop checking = instrument functionality test its means the instrument is in running condition if any fault may occur r not its should be make sure
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / ajinkya
I think...
Cold loop test is done using simulator
Hot loop test is done actually in field
| Is This Answer Correct ? | 6 Yes | 63 No |
Answer / jaydip khatri
hot loop mean instrument to J.B. & cold loop mean J.B. to panal.
| Is This Answer Correct ? | 5 Yes | 73 No |
what is thermo coupler and how it works
how we calculate the range of flow from a dp?i mean if we have a dp,3810mm h2o.how much flow ranges we can use for this DP?
plz give me the logic for how a pushbuttoon can be worked as atoggle switch i m working with allenbradely/micrologix1200/rslogix500
I have 0.75mm sq multicore cable (IS type) , can use instead of same type but 1.5 sq mm cable ? Note : The distance is around about 150 meter.
what is the basic working principle of I/P and Positioner in any control valve.
Can 2 transmitters be connected to Integral orifice meter taps? Does an integral orifice comes with 2 set of taps?
wht is loops ? how many loops are there?
I have one DP transmitter of range 0-500mmWC i have to calculate its range in M3/hr for flow measurement so whats the formula.
what is full form of NAK?
why pressure 3-15psi is used as industrial standard and what is the reason
2 Answers JAL International, UltraTech,
how u calibrate pneumatic n motorized c/v?
what is the difference between E/P positioner and I/P positioner in control valve , in which application the respective positioner are used in.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)