Answer / sriram

the transmission of electrical energy have some losses. if
we step down directly from 33kv to 415v. the resulting
voltage may only an under voltage. in order to avoid that
we have some restrictions.

Is This Answer Correct ?    92 Yes 36 No

why we step down voltage level from 33kv to 11kv and 11kv to 415v.Instead we can step down voltage..

Answer / anonymous

11kv is basically for primary distribution say to a large
factory. so at a substation, stepping down to 11kv for such
use and further stepping down to 415V for residential areas.

Is This Answer Correct ?    64 Yes 21 No

why we step down voltage level from 33kv to 11kv and 11kv to 415v.Instead we can step down voltage..

Answer / kiran

It is not advisable to step down directly for following
reasons.
a) If insulation between 33kV and 415V winding fails, then
before triping, for a fraction of second 33kV high voltage
will get connected to 415V system, on which vast users &
equipments are connected.
b) Fault level on 33 kV is more, hence if fault occures on
415V bus side, heavy kA fault current will flow as compared
to 11kV/415V transformer.


But nowadays, 33kV/415V transformers are widely used to
avoid double transformers

Is This Answer Correct ?    73 Yes 35 No

why we step down voltage level from 33kv to 11kv and 11kv to 415v.Instead we can step down voltage..

Answer / nikul polara

when we use this type of system we provide in cable
insulation level is very high and we dont use 11kv in
industrial area.

Is This Answer Correct ?    8 Yes 10 No

why we step down voltage level from 33kv to 11kv and 11kv to 415v.Instead we can step down voltage..

Answer / lee onn

It is cause the wagamama theory. 1+1 =3

Is This Answer Correct ?    2 Yes 5 No

why we step down voltage level from 33kv to 11kv and 11kv to 415v.Instead we can step down voltage..

Answer / sunil walia

In the past the Electricity take over points were at 11 KV
and feeders used to be 11 KV feeders. Stepping down to 415 V
was done for individual pockets. Subsequently State
electricity boards mandated that electric supply will be
given at 33 KV or above depending on load. Hence, takeover
was converted to 33KV, However the old 11KV feeders were not
replaced. So stepping down was done in two stages ie
33KV/11KV and 11KV/415V. Now in some all new townships
33KV/415V is being with feeders at 33KV. However, this is
limited because of the ambient quality and cost of 33KV
cables, switch gear etc. Considering the industrial quality
and output 33KV/11KV and 11KV/415V circuits shall be used.

Is This Answer Correct ?    12 Yes 16 No

why we step down voltage level from 33kv to 11kv and 11kv to 415v.Instead we can step down voltage..

Answer / raviteja nowduru

a)in a 33/11 kv transformer has more current on secondary.if
it is 33/.415 kv much more current in secondary .so
conductors on secondary should be designed to 415v ,and for
a large current.
But if it is 33/11kv transformer they will be distributed
to various 11/.415 kv transformers.so current capacity of
conductors are decreased.

Is This Answer Correct ?    8 Yes 12 No

why we step down voltage level from 33kv to 11kv and 11kv to 415v.Instead we can step down voltage..

Answer / hosam

33kv to 11kv 20MvA 2TX 415v 16MW & 33kv to .433v pole mounted or Ground mounted tx 1000kva/.433 voltage increased between 33kv to 11kv that why use tx 33kv11kv we can use also 66kv to 33kv and 6.6kv with 33kv to 6.6kv cable connection 3Cx300mm.sq for 33kv and 11kv use to connection 3Cx240mm.sq.

Is This Answer Correct ?    0 Yes 4 No

why we step down voltage level from 33kv to 11kv and 11kv to 415v.Instead we can step down voltage..

Answer / gulshan goyal(knit->iitk)

distribution transformer energised 24 hours hence there
are continious core losses which in turn depends on
voltage.Hence to reduce core losses transformer is
energised 24 hours at lower(11kv) voltage.

Is This Answer Correct ?    12 Yes 18 No

why we step down voltage level from 33kv to 11kv and 11kv to 415v.Instead we can step down voltage..

Answer / rakesh singh

The fault level of 33 KV/.415KV transformer is less as
compaired to the 11KV/.415KV.So during the faulty
conditions the fault current will be high in the first case
and for the lighting circuit we will have to put lighting
transformers to reduce the fault level up to the fault with
stand capacity of lighting switch gears which are available
up to 10 KA only.
But for the power circuit i.e for MCC and PMCC for whitch
switch gear of 35 KA and 50 KA are available we can use 33
KV/.415KV transformer loking to our total load and
availabilty of supply at 33 KV volatage level.

Is This Answer Correct ?    7 Yes 16 No

Post New Answer

More Electrical Engineering Interview Questions

why power factor is lagging and leading(i.e -1to +1)

2 Answers  


How to calculate the NGR value for a 2.7MVA Transfomer, 11KV system where the fault current has to be limited to 50A?

1 Answers   Sterling Wilson,


why two contacts(in series) are using in closing circuit

3 Answers  


Why is it prefer to initiate circuit breaker failure by "86" lockout relay not by "94" tripping relay ?!

0 Answers   OEG,


wHAT IS CAPACITANCE LATCHING? hOW TO CALCULATE CAPACITANCE LATCHING? hOW TO SOLVE THE PROBLEM IF CAPACITANCE LATCHING APPLIED?

0 Answers  






which type of A.C motor is used in the fan (ceiling fan, exhaust fan, padestal fan, bracket fan etc) which are find in the houses ?

25 Answers   Airtel, MPPTCL, USSA,


what is need of air gap in expansion section in busbar?

3 Answers  


what is the maximum genarating in india?

17 Answers  


What is the formula to calculate the rating of power cable for three phase current.

0 Answers  


Why does the power consumed is always constant even if a fan speed is altered?

5 Answers  


Single phase and threephase power calculation

0 Answers  


why the protection turbo generators is most complex?

0 Answers   Infres, L&T,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)