why we step down voltage level from 33kv to 11kv and 11kv
to 415v.Instead we can step down voltage from 33kv to 415v
directly using single transformer.
Answers were Sorted based on User's Feedback
Answer / sriram
the transmission of electrical energy have some losses. if
we step down directly from 33kv to 415v. the resulting
voltage may only an under voltage. in order to avoid that
we have some restrictions.
| Is This Answer Correct ? | 92 Yes | 36 No |
Answer / anonymous
11kv is basically for primary distribution say to a large
factory. so at a substation, stepping down to 11kv for such
use and further stepping down to 415V for residential areas.
| Is This Answer Correct ? | 64 Yes | 21 No |
Answer / kiran
It is not advisable to step down directly for following
reasons.
a) If insulation between 33kV and 415V winding fails, then
before triping, for a fraction of second 33kV high voltage
will get connected to 415V system, on which vast users &
equipments are connected.
b) Fault level on 33 kV is more, hence if fault occures on
415V bus side, heavy kA fault current will flow as compared
to 11kV/415V transformer.
But nowadays, 33kV/415V transformers are widely used to
avoid double transformers
| Is This Answer Correct ? | 73 Yes | 35 No |
Answer / nikul polara
when we use this type of system we provide in cable
insulation level is very high and we dont use 11kv in
industrial area.
| Is This Answer Correct ? | 8 Yes | 10 No |
Answer / sunil walia
In the past the Electricity take over points were at 11 KV
and feeders used to be 11 KV feeders. Stepping down to 415 V
was done for individual pockets. Subsequently State
electricity boards mandated that electric supply will be
given at 33 KV or above depending on load. Hence, takeover
was converted to 33KV, However the old 11KV feeders were not
replaced. So stepping down was done in two stages ie
33KV/11KV and 11KV/415V. Now in some all new townships
33KV/415V is being with feeders at 33KV. However, this is
limited because of the ambient quality and cost of 33KV
cables, switch gear etc. Considering the industrial quality
and output 33KV/11KV and 11KV/415V circuits shall be used.
| Is This Answer Correct ? | 12 Yes | 16 No |
Answer / raviteja nowduru
a)in a 33/11 kv transformer has more current on secondary.if
it is 33/.415 kv much more current in secondary .so
conductors on secondary should be designed to 415v ,and for
a large current.
But if it is 33/11kv transformer they will be distributed
to various 11/.415 kv transformers.so current capacity of
conductors are decreased.
| Is This Answer Correct ? | 8 Yes | 12 No |
Answer / hosam
33kv to 11kv 20MvA 2TX 415v 16MW & 33kv to .433v pole mounted or Ground mounted tx 1000kva/.433 voltage increased between 33kv to 11kv that why use tx 33kv11kv we can use also 66kv to 33kv and 6.6kv with 33kv to 6.6kv cable connection 3Cx300mm.sq for 33kv and 11kv use to connection 3Cx240mm.sq.
| Is This Answer Correct ? | 0 Yes | 4 No |
Answer / gulshan goyal(knit->iitk)
distribution transformer energised 24 hours hence there
are continious core losses which in turn depends on
voltage.Hence to reduce core losses transformer is
energised 24 hours at lower(11kv) voltage.
| Is This Answer Correct ? | 12 Yes | 18 No |
Answer / rakesh singh
The fault level of 33 KV/.415KV transformer is less as
compaired to the 11KV/.415KV.So during the faulty
conditions the fault current will be high in the first case
and for the lighting circuit we will have to put lighting
transformers to reduce the fault level up to the fault with
stand capacity of lighting switch gears which are available
up to 10 KA only.
But for the power circuit i.e for MCC and PMCC for whitch
switch gear of 35 KA and 50 KA are available we can use 33
KV/.415KV transformer loking to our total load and
availabilty of supply at 33 KV volatage level.
| Is This Answer Correct ? | 7 Yes | 16 No |
How to do maintenance of transformer feeder.
In LT Line What is the minimum clearance required between phase to phase busbar & between Phase to body of the panel? Also between Neutral &phase, & Neutral & body of panel. as per standards.
hey guys i scored 910 on GRE and 67 on TOEFL respectively.I have an aggregate of about 74%in my B tech.For which colleges should i apply for an MS program in electrical engineering.I am looking for colleges in NJ,SC,NC,GEORGIA, NY. Please reply with a good response.....
what modulation is used in landline telephone signals?
what is high - pot test. what's its use?????
Why a ballast and ignitor is required in MH and other lighting fixtures
what are the materials used in HRC fuse
In transmission line the line power loss only accured at resistance the inductance and capacitance wont consume power is it correct?
what will happen if we use cylindrical conductor instead of flat cu conductor in transformer
Write the programming software name for LG, SIEMENS,Messung,AB
what is an S.C.R. and how do they work?
Give some example of fault limiting devices?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)