What is RTCC in a transfomer and specify its function.
Answers were Sorted based on User's Feedback
Answer / yash
RTCC is Remote Tap Change Circuit is connected to OLTC of
Transformer through control cables. It raise & lower the
voltage as accordingly specified by controlling the motor
drive in OLTC electrically (and manually through Push
Buttons)
In RTCC an AVR (Automatic Voltage Regulator)is fixed to
maintain the output voltage level(raise & lower) by
controlling the motor.
| Is This Answer Correct ? | 369 Yes | 21 No |
Answer / sanketh
RTCC is a panel it should be place in the electrical room
for Remote Tap changing.It must Required while OLTC is used.
| Is This Answer Correct ? | 201 Yes | 19 No |
Answer / joy banerjee
In transformers Output Voltage can be controlled either by
Off Circuit Tap Changer (Manual tap changing)or By On -
Load Tap Changer-OLTC (Automatic Changing).
In the transformer with OLTC, it is a closed loop system,
with follwing components:
#1. AVR (Automatic Volatge Regulator- an electronic
programable device). With this AVR we can set the Output
Voltage of the transformers. The Output Voltage of the
transformer is fed into the AVR through the LT Panel. The
AVR Compares the SET voltage & the Output Voltage and gives
the error signal, if any, to the OLTC through the RTCC
Panel for tap changing. This AVR is mounted in the RTCC.
#2. RTCC (Remote Tap Changing Cubicle):This is a panel
consisting of the AVR, Dispaly for Tap Position, Voltage,
LEDs for Raise & Lower of Taps relays, Selector Switches
for Auto Manual Selection... In AUTO MODE the voltage is
contrlled by the AVR. I manual Mode the operator can
Increase / decrease the voltage by changing the Taps
maually through the Push Button in the RTCC.
#3. OLTC is mounted on the transfomer. It consits of a
motor, controlled by the RTCC, which changes the Taps in
the transformers.
| Is This Answer Correct ? | 111 Yes | 7 No |
Answer / arun babu.s
RTCC is " Remote Tap Change Centre " which is a
programmable device to control the output of the transfomer
thro'OLTC unit fitted in the transformer through control
cables.
The desired voltage will be achieved accordingly by
controlling the OLTC with respect to the tap position
through RTCC system.
The output voltage of the transformer is been maintained
through an inbuilt AVR (Automatic Voltage Regulator),which
continuously verifies the output power with the set /
programmed reference voltage.Which triggers the OLTC
accordingly.
Hence,by above said phenomena,the consistency of the
transformer output is been maintained.
| Is This Answer Correct ? | 70 Yes | 9 No |
Answer / rahul kumar
In transformers Output Voltage can be controlled either by
Off Circuit Tap Changer (Manual tap changing)or By On -
Load Tap Changer-OLTC (Automatic Changing).
In the transformer with OLTC, it is a closed loop system,
with follwing components:
#1. AVR (Automatic Volatge Regulator- an electronic
programable device). With this AVR we can set the Output
Voltage of the transformers. The Output Voltage of the
transformer is fed into the AVR through the LT Panel. The
AVR Compares the SET voltage & the Output Voltage and gives
the error signal, if any, to the OLTC through the RTCC
Panel for tap changing. This AVR is mounted in the RTCC.
#2. RTCC (Remote Tap Changing Cubicle):This is a panel
consisting of the AVR, Dispaly for Tap Position, Voltage,
LEDs for Raise & Lower of Taps relays, Selector Switches
for Auto Manual Selection... In AUTO MODE the voltage is
contrlled by the AVR. I manual Mode the operator can
Increase / decrease the voltage by changing the Taps
maually through the Push Button in the RTCC.
| Is This Answer Correct ? | 35 Yes | 3 No |
Answer / praveen
RTCC is Remote tap changer circuit, normaly RTCC panel will
be installed in Main panel room and will be connected to
OLTC ( On line tap changer) of the transformer through
control cable.There will be AVR in RTCC Panel to control
the secondary voltage of the transformer and AVR output
will control OLTC motor in Clock wise or Anty clock wise.
and also there will be selection in RTCC panel for Auto and
manual operation.
| Is This Answer Correct ? | 32 Yes | 7 No |
Answer / lalit pratap
RTCC full form is (Remote tap change Control) it's using in OLTC (On Load Tap Changer)installed transformers for voltage regulation controll.
| Is This Answer Correct ? | 23 Yes | 1 No |
Answer / rajeev
RTCC refers to Remote tap changer cubicle.
It is used to change the tap of transformer from LT panal
room whith the help of remote circuit.
| Is This Answer Correct ? | 27 Yes | 6 No |
Answer / ajay kumar singh
RTCC IS REMOTE TAPCHANGER CONTROL CUBICAL WHICH IS ESTABLISH IN CONTROL ROOM OF SUBSTATON, IT IS REQUIRED WHEN OLTC IS USE IN POWER TRANSFORMER,AVRR(AUTOMATIC VOLTAGE REGULATER RELAY)MOUNTED ON RTCC PANEL WHICH SET UP SECONDARY VOLTAGE OF TRANSFORMER FOR AUTO MODE ONLY
| Is This Answer Correct ? | 16 Yes | 5 No |
Answer / anand
RTCC IS REMOTE TAP CHANGE CUBICLE , WHICH GOVERNS THE
VOLTAGE CONTROL OF THE TRANSFORMER THROUGH AVR OR BY MANUALLY.
IT HAS ANNUNCIATOR (MICROPROCESSOR BASED PROGRAMMING)WHICH
ALARMS THE OPERATOR DURING THE FAILURE OF FAN ETC.
| Is This Answer Correct ? | 12 Yes | 7 No |
what is the pre commissioning test to be carried out on LT power panel at site?
Why celling fan rotates in anticlockwise direction and table fan in clockwise direction ? Give technical reason.
what is the use of terminals in transformer ?
1 Answers Core Solutions, Honeywell,
What is minimum permicible value of leackage current for LT Panle when applying voltage up to 3 KV for 5 Minuits?
why the starting current of a motor is high?
What is method of calculating the fault current for a MDB, 50KW, 3PH, 415V, 50HZ?
In our domestic single phase line if you don't have a ground connection (earthing)how will you separately use earth in a specific power supply board.
. What should be the minimum and maximum ohmic value for earthing?
What is size 00, 01, 1 etc., in HRC fuse types?
Dear Sir/Madam, I have one questions we have three steam turbines and one Gas turbine and our industry linked with the public network, we have protection system one of the protection is reverse power we can export just four MW only i would like to ask about how to calculate the reverse power. Thank you in advance best regards
If not maintained 3 phase clearance,what happened ?
i have 6oo kva dry type transformer and its neutral is not grounded even body of transformer ground i want to know it is safe or not ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)