CURRENT DENSITY OF CU=1.2A/MM2
CURRENT DENSITY OF AL=.8A/MM2
FOR EX: DESIGN REQUIREMENT OF 400A MAX.CAPACITY.
CONSIDER THE BUSBAR IS CU.
AREA OF THE BUSBAR=400A/1.2=333.33MM2
APPROX. VALUE= 350MM2
SO THAT, THE STANDARD SIZE IS 50MMX8MM
| Is This Answer Correct ? | 33 Yes | 9 No |
Answer / khan
Usually busbar sizes selection depends mainly on two
factors. Which is current + temperature. The size which you
are going to select must carry the current you need and
must not create much heat which excess the limits.
Our formula , we use 1.5 A / 1 sqmm.
| Is This Answer Correct ? | 28 Yes | 9 No |
Answer / jk
Aluminum current transfer capacity :0.8 amps/sq mm
Copper current transfer capacity :1.6 amps/sq mm
Example:640 amps
x= 640 / .8 = 800 sq mm
800/10 (Say 10 mm Width)
L=80 MM, W=10 MM
| Is This Answer Correct ? | 17 Yes | 5 No |
Answer / jad
Please Give the references........otherwise its very
confusing....!
| Is This Answer Correct ? | 12 Yes | 1 No |
Answer / renukaswamy
We have consider so many factors to calculate Busbar sizing.
a) Current carrying capacity : for that Copper can go upto
1.6A/Sq.mm and Aluminium is 1A/Sq.mm
b) Ambient temp. and temp. rise to considered.
c) Heat loss to be considered.
d) Short circuit current to be considered.
| Is This Answer Correct ? | 12 Yes | 1 No |
Answer / dubai
The bus bar size normally for copper 1sqmm=1.25Amp and
aluminium is 1sqmm=0.8Amp
| Is This Answer Correct ? | 9 Yes | 2 No |
Answer / karim halawa
simply the dinesty of the copper equal 2A/mm2 or 1.5A/mm2
accprding purity of the substance so using mentioned
formula to get size of bus bar .
| Is This Answer Correct ? | 8 Yes | 2 No |
Answer / gajanan
I want to ask to vijay that is there any relation between
current denesity of copper and material purity.
also is ther any standard which defines the standard
current denesity of material.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / rohit bhardwaj
Thumb rule for copper is 1.25 Amps per sq.mm and for Aluminum 0.8 amps for sq.mm
| Is This Answer Correct ? | 8 Yes | 3 No |
why armature is placed in stator but not in rotor in synchronous generator ?
difference btw neutral and ground?
why semiconductor fuse used in drive ,not ordinary?
how to compute kvar in substation feeder to improve power factor and sending voltage
what mean by power factor
If a motor of 30KW rating &200 mtrs distance from feeder give me the cable size selection calculation?
How to size fuse? How to size MCB?
i need bhel question papers.
wht is this amps in power consuption and how can we convert that into consuption hours ? i am a sales executive of a energy saving lamps .
what is the significance of tan&delta and how it performed in power transformer
what is voltage,current,restance,. what is single phase&three phase motar. what is basic electrical 'farmoulas. what is defirens quetions of electrical maintenance.
what are trouble functions of transformer?ex. prv trip,oltc,oti,wti.explain detail.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)