How to calculate busbar size & what is the procedure we
make for determine that?
Answers were Sorted based on User's Feedback
CURRENT DENSITY OF CU=1.2A/MM2
CURRENT DENSITY OF AL=.8A/MM2
FOR EX: DESIGN REQUIREMENT OF 400A MAX.CAPACITY.
CONSIDER THE BUSBAR IS CU.
AREA OF THE BUSBAR=400A/1.2=333.33MM2
APPROX. VALUE= 350MM2
SO THAT, THE STANDARD SIZE IS 50MMX8MM
| Is This Answer Correct ? | 33 Yes | 9 No |
Answer / khan
Usually busbar sizes selection depends mainly on two
factors. Which is current + temperature. The size which you
are going to select must carry the current you need and
must not create much heat which excess the limits.
Our formula , we use 1.5 A / 1 sqmm.
| Is This Answer Correct ? | 28 Yes | 9 No |
Answer / jk
Aluminum current transfer capacity :0.8 amps/sq mm
Copper current transfer capacity :1.6 amps/sq mm
Example:640 amps
x= 640 / .8 = 800 sq mm
800/10 (Say 10 mm Width)
L=80 MM, W=10 MM
| Is This Answer Correct ? | 17 Yes | 5 No |
Answer / jad
Please Give the references........otherwise its very
confusing....!
| Is This Answer Correct ? | 12 Yes | 1 No |
Answer / renukaswamy
We have consider so many factors to calculate Busbar sizing.
a) Current carrying capacity : for that Copper can go upto
1.6A/Sq.mm and Aluminium is 1A/Sq.mm
b) Ambient temp. and temp. rise to considered.
c) Heat loss to be considered.
d) Short circuit current to be considered.
| Is This Answer Correct ? | 12 Yes | 1 No |
Answer / dubai
The bus bar size normally for copper 1sqmm=1.25Amp and
aluminium is 1sqmm=0.8Amp
| Is This Answer Correct ? | 9 Yes | 2 No |
Answer / karim halawa
simply the dinesty of the copper equal 2A/mm2 or 1.5A/mm2
accprding purity of the substance so using mentioned
formula to get size of bus bar .
| Is This Answer Correct ? | 8 Yes | 2 No |
Answer / gajanan
I want to ask to vijay that is there any relation between
current denesity of copper and material purity.
also is ther any standard which defines the standard
current denesity of material.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / rohit bhardwaj
Thumb rule for copper is 1.25 Amps per sq.mm and for Aluminum 0.8 amps for sq.mm
| Is This Answer Correct ? | 8 Yes | 3 No |
wow to calculate the transformer rating(KVA)
Petroleum jelly is applied to the terminals of the lead acid battery is to prevent?
Transformer TTR test procedure
which connection is safer series or parallel?usually which connection we prefer at home?
In general bus riser follows the bus section in SWGR. What are impacts if bus section follows bus riser?
Why a starter is used for a motor?
50 Answers L&T, Nilachal Polytechnic,
In Single Phase AC Supply,If Voltage between Phase and Neutral is 230V means what will be the Voltage between Phase and Earth?
how Local Breaker Backup relay working?
In which type of circuit short circuit is dangerous in parallel or series and why?
What is the name of the winding from which the supply is taken for load connections?
Is there any problem about which the drive (inverter) doesn't show/display the alarm and/or fault but instead of this , it doesn't work ? I want to know that could there be any kind of problem in the drive when the drive doesn't display the alarm and/or fault ?
Can we perform parallel operation of two transformers when one transformer on load?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)