Answer / shilesh kumar
Generally current carrying capacity of Al. is 0.8A per
sqmm and Copper is 1.6A per Sqmm.
Suppose we need bus bar for 630A, and we are going with
Aluminium bus bar
= 80*10*.8=640A
where 80*10 is size if bus bar usually available is the
market.
so we can use 80x10sqmm al. busbar per phase for 630A.
for TPN- (3.5)x80x10
If we are going with Copper bus bar
than we will use = 40x10sqmm per phase
= 40x10x1.6=640A
where 40*10 is size if bus bar usually available is the
market.
so we can use 40x10sqmm copper busbar per phase for 630A.
for TPN- (3.5)x40x10
| Is This Answer Correct ? | 0 Yes | 1 No |
Depending on the maximum load current the busbar size will
be determined. Usually for copper it is taken as 2 to 4 Amps
per square mm and for alluminium it is taken as 1 to 2 Amps
per sqmm.
The normal availability and design of the busbars is
25*5mm,50*5mm,50*10mm,60*10mm.
| Is This Answer Correct ? | 57 Yes | 61 No |
Answer / john philip
As per the load we have to calculat but we should choos a
good conducter with low resistenc value
| Is This Answer Correct ? | 11 Yes | 16 No |
Answer / hasan 325
to calculate bus bar u must follow this formula :
wiedth x thickness x1.6 A
And also u can use this information :
A/mm2
100A = 2.5mm2
100-500 A=1.75mm2
500-1000A=1.2mm2
1000-above=1.1mm2
| Is This Answer Correct ? | 40 Yes | 80 No |
How does one convert an AC motor into a generator?
WHAT IS THE DIFFERENCE BETWEEN SHOP DRAWINGS/ DESIGN DRAWINGS AND AS BUILT DRAWINGS??
2 Answers ACC, Al-Jaber, Dubai Group, ECEC,
how we can calcultae the short circuit level for bus bar
0 Answers Jaiprakash, Panorama Apparels,
What is the type of electrical earthing recommended in hard rock area
What will be the resultant out put voltage when two different voltage rating batteries are vconnected in parallel? pls. answer with example if available.
What is the requirement of grounding the neutral of single phase generators on load? If the neutral is not grounded, what will be the effect?
When connecting a loaded powerplant to the Huge grid,what are the factors to be considered and how the VAR flow will affect the system?
What will happen if the generator turns in a wrong direction?
Why transformer making noise during the operation?
Any one can explaination about calibration with rotating sub standards?
plz tell me,ht and lt panel terminals in substations explain beiefly
What is double delta conection in AC Motor? And can we done the double RPM of the motor by double delta conection?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)