Answer / pradhyumn
OTI stands for Oil Temperature Indicator and WTI stands for
Winding Temperature Indicator. They are used for
Transformer protection.The temperature of winding increases
as the load increases. Oil is used as coolant for the
winding so as winding heats up oil temp. rises as well.
The life of transformer depends on insulating material
between the windings so it is important to check and
control the temp. OTI and WTI are thus used for alarm or
tripping of the transformers.
Is This Answer Correct ? | 39 Yes | 10 No |
Answer / rizwan
A basic or Avg Difference in OTI & WTI are, :- WTI needs a
CT to function , While OTI does not need a CT. WTI has both
Alarm & Trip , Though OTI also has both ALarm & Trip , there
is also a OTI without Alarm & Trip . Its not the cas of WTI.
Is This Answer Correct ? | 15 Yes | 9 No |
Answer / c.d.elkunchwar
There is no fix differnce as such.Itdepends upon the
transformer tempareture gradiant at that current, specified
by the manufacturer.the difference between ot&wt varies as
per load and gradient.Normally it can be from 12 to 16
degrees at full load.
Is This Answer Correct ? | 7 Yes | 3 No |
Answer / k.prakashchandra
The above answer given by me is not true in all cases.Those
were the readings recorded on 220/110 KV auto
transformer.The WT is higher than OT as WTI is close to the
source of heat.The difference between WT and OT depends on
cooling and oil circulation.More the difference worse the
cooling efficiency.The difference is about 20 %(220 KV) to
40% (110KV) of temperature rise in WT ,as observed in case
of the above Tr.But WT of tertiary was found to be less than
the OT
Is This Answer Correct ? | 4 Yes | 5 No |
Answer / boss
it was correct answar, but ct current rating has been deppond on trasformer manufacture.
Is This Answer Correct ? | 0 Yes | 2 No |
WHAT IS THE USAGE OF Buckoltz relay IN POWER TRANSFORMER AND AND HOW ITS FUNCTIONS?
In batteries after completion of charging which colour gas is emitted from it?
Why Lightning arrester used? Can we use piece of iron as a core material of transformer, if No, why? In CRGOSS material what is meaning of cold rolled grain oriented? Why Impegrenation of Transformer is done? Properties of Insulator? what is phase angle? Testing of transformers (Routine & Monthly)?
What is Surge Capacitor? Why it is require in Generator Circuit Breaker,inspite of surge arrester?
234 MVA Generator 3 phase Short circuit current Values required? Gen set Rating-234 MVA, Gen Voltage-18kv, PF;0.8, Xdv:23.5 %, Transformer Rating-18/380KV, 680MVA,Yndd1 two winding, Step up TR, ZT:35.50 %,X/R 4.33 Gen CB Position, CB open ,Disconnected open, Generator Running Voltage 18 Kv, Bi mistakes generator side earth switch Closed during that time short circuit current level in 3 Phase required, and how to test on site 234MVA Generator Short circuit current,
why cant we use earth as neutral at home whereas neutral is actually grounded at transformer end?
is oil viscosity affect on motor current?
how to read AWG n how to convert AWG reading into mm?
what is alluminium arm in ab conductors
In siemens S7-300 PLC, what is function and function block ? What is the difference between them ? When to use function and when to use function block ?
What size cable is used for HT cable to the transformer of 630kVA, and the supply voltage is 11kV
In case of dc circuit Whether dc current will pass through capacitor after it gets charged?