How to calculate busbar size & what is the procedure we
make for determine that?
Answer Posted / santhoshsasidharan
CURRENT DENSITY OF CU=1.2A/MM2
CURRENT DENSITY OF AL=.8A/MM2
FOR EX: DESIGN REQUIREMENT OF 400A MAX.CAPACITY.
CONSIDER THE BUSBAR IS CU.
AREA OF THE BUSBAR=400A/1.2=333.33MM2
APPROX. VALUE= 350MM2
SO THAT, THE STANDARD SIZE IS 50MMX8MM
| Is This Answer Correct ? | 33 Yes | 9 No |
Post New Answer View All Answers
How phase to phase voltage comes 440V.
In general bus riser follows the bus section in SWGR. What are impacts if bus section follows bus riser?
what is the formula of starting current of 3phase and 1 phase motor???
what is meant by motor startup supervision & motor load jam protection ?
How can I model an open-delta ground transformer for a network supplied by 4 unit GTG and power transformer in ETAP?
How many types are using in 220kv/400 kv swith yard
what is the formula for efficiency of francis turbine and generator for hydropower? what is best way to select francis turbine and generator?
what curve and rateing would you use for a three phase 0.75kw motor?
What is meant by celling voltage & current in excitor ?
What is slope...? Explain slope 1 and slope 2...?
if we have a industrial load of 400 kilowatts with 415 volt AC then how much total harmonic distortion (thd%) should be acceptable for steady power system.
If I want to lift the water at a height 50m from ground level through two inch(diameter) metal pipe then what is the capacity of motor pump is required? is it possible in single phase supply or not?
what is inter connected dc generator?
which type of stability limit is higher,steady state or transient? why?
explain types of electric welding and its applications