How to calculate busbar size & what is the procedure we
make for determine that?
Answers were Sorted based on User's Feedback
Answer / sujata wagh
Generally current carrying capacity of Al. is 0.8A per
sqmm and Copper is 1.6A per Sqmm.
Suppose we need bus bar for 630A, and we are going with
Aluminium bus bar
= 80*10*.8=640A
where 80*10 is size if bus bar usually available is the
market.
so we can use 80x10sqmm al. busbar per phase for 630A.
for TPN- (3.5)x80x10
If we are going with Copper bus bar
than we will use = 40x10sqmm per phase
= 40x10x1.6=640A
where 40*10 is size if bus bar usually available is the
market.
so we can use 40x10sqmm copper busbar per phase for 630A.
for TPN- (3.5)x40x10
| Is This Answer Correct ? | 246 Yes | 46 No |
Answer / ashraf majid
The busbar size will be determined by the total loads
connected to the bus.This will require a comprehensive
study of nature of loads plus the surroundings of place.
The general procedure will be such that the operating
parameters don't voilate the maximum safety limits of the
bus.
| Is This Answer Correct ? | 145 Yes | 65 No |
Answer / kajajohn
to calculate bus bar size normally for copper 1 sqmm =1.3 A
for aluminium 1 sqmm =0.8 Amps
| Is This Answer Correct ? | 129 Yes | 49 No |
Answer / bhavin shah
busbar sizes can not be calculated only from overall size.
there are various derating factors like arrangment of
busbar, nos of busbar, spacing, enclouser size, ventilation
in room, temp rise, skin effect, proximity effect etc.
which need to be consider while designing the busbar.
| Is This Answer Correct ? | 64 Yes | 15 No |
Answer / akmal
i want to add in vijay answer that the qulity of copper also
depend on amper rating of coper bar
| Is This Answer Correct ? | 65 Yes | 22 No |
Answer / jaydev jena
current density= .8 amp/sqmm.that does mean 1sqmm can carry
0.8 amp current .if sisze of busbar is 100mmx 10 mm then it
can carry 800 amp.
| Is This Answer Correct ? | 61 Yes | 25 No |
Answer / nikhan
The bus bar size normally for copper 1sqmm=1.3Am and
aluminium is 1sqmm=0.8Amp
| Is This Answer Correct ? | 53 Yes | 20 No |
Answer / waves
Generally current carrying capacity of Al. is 0.8A per
sqmm and Copper is 1.6A per Sqmm.
Suppose we need bus bar for 630A, and we are going with
Aluminium bus bar
= 80*10*.8=640A
where 80*10 is size if bus bar usually available is the
market.
so we can use 80x10sqmm al. busbar per phase for 630A.
for TPN- (3.5)x80x10
If we are going with Copper bus bar
than we will use = 40x10sqmm per phase
= 40x10x1.6=640A
where 40*10 is size if bus bar usually available is the
market.
so we can use 40x10sqmm copper busbar per phase for 630A.
for TPN- (3.5)x40x10
| Is This Answer Correct ? | 40 Yes | 7 No |
can you give any example at any parameters?
| Is This Answer Correct ? | 62 Yes | 37 No |
Answer / md.mahmudul hasan
we need to consider short ckt(KA) also. Say short ckt level
is 20KA then we need to select busbar accordingly.
| Is This Answer Correct ? | 30 Yes | 5 No |
what is the difference between STAR and DELTA connection and application wise how it can be utilizedd
Why are iron cores in transformers made laminated?
WHAT IS FORMULA TO KNOW TO BACKUP TIME OF POWER PLANT 48V/50AMP DELTA POWER PLANT
What is transformer break down voltage.And what is flash oil flash point.
What happen to generator if i have unbalanced load?
1 Answers Reliance Energy, Sail, TCS,
What is different between Regulator & Stabilizer?
Draw SLD feeding from the SS up to distribution board of the load, calculate cable size, breaker sizes, and meter for the following case: Ground Floor: electric room, pump room, 5 shops, each is 15 KW First Floor: 5 shops, each is 15 KW Second Floor: showroom 30 KW Service Loads: water pump 3 KW (3ph) , fire pump 3 KW (3ph), and one DB service 12 KW (3ph).
what is function of rtu?
FULL FORM OF MCCB
if a single phase 3 hp submersible pump of Crompton Greaves is moving in reverse direction and sometimes it moves in rigth direction ,then what may be the cause....
The armature of shunt dc motor has 0.8ohm resistance and motor is to run on 120V circuit.If motor is suddenly thrown on circuit while armature at standstill then current drawn by motor will be??Also back emf in normal running is 110V
why substation rating interms of 11 multiples???like 11kv/33kv iis there any special reason???
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)