How to calculate busbar size & what is the procedure we
make for determine that?
Answers were Sorted based on User's Feedback
Answer / sujata wagh
Generally current carrying capacity of Al. is 0.8A per
sqmm and Copper is 1.6A per Sqmm.
Suppose we need bus bar for 630A, and we are going with
Aluminium bus bar
= 80*10*.8=640A
where 80*10 is size if bus bar usually available is the
market.
so we can use 80x10sqmm al. busbar per phase for 630A.
for TPN- (3.5)x80x10
If we are going with Copper bus bar
than we will use = 40x10sqmm per phase
= 40x10x1.6=640A
where 40*10 is size if bus bar usually available is the
market.
so we can use 40x10sqmm copper busbar per phase for 630A.
for TPN- (3.5)x40x10
| Is This Answer Correct ? | 246 Yes | 46 No |
Answer / ashraf majid
The busbar size will be determined by the total loads
connected to the bus.This will require a comprehensive
study of nature of loads plus the surroundings of place.
The general procedure will be such that the operating
parameters don't voilate the maximum safety limits of the
bus.
| Is This Answer Correct ? | 145 Yes | 65 No |
Answer / kajajohn
to calculate bus bar size normally for copper 1 sqmm =1.3 A
for aluminium 1 sqmm =0.8 Amps
| Is This Answer Correct ? | 129 Yes | 49 No |
Answer / bhavin shah
busbar sizes can not be calculated only from overall size.
there are various derating factors like arrangment of
busbar, nos of busbar, spacing, enclouser size, ventilation
in room, temp rise, skin effect, proximity effect etc.
which need to be consider while designing the busbar.
| Is This Answer Correct ? | 64 Yes | 15 No |
Answer / akmal
i want to add in vijay answer that the qulity of copper also
depend on amper rating of coper bar
| Is This Answer Correct ? | 65 Yes | 22 No |
Answer / jaydev jena
current density= .8 amp/sqmm.that does mean 1sqmm can carry
0.8 amp current .if sisze of busbar is 100mmx 10 mm then it
can carry 800 amp.
| Is This Answer Correct ? | 61 Yes | 25 No |
Answer / nikhan
The bus bar size normally for copper 1sqmm=1.3Am and
aluminium is 1sqmm=0.8Amp
| Is This Answer Correct ? | 53 Yes | 20 No |
Answer / waves
Generally current carrying capacity of Al. is 0.8A per
sqmm and Copper is 1.6A per Sqmm.
Suppose we need bus bar for 630A, and we are going with
Aluminium bus bar
= 80*10*.8=640A
where 80*10 is size if bus bar usually available is the
market.
so we can use 80x10sqmm al. busbar per phase for 630A.
for TPN- (3.5)x80x10
If we are going with Copper bus bar
than we will use = 40x10sqmm per phase
= 40x10x1.6=640A
where 40*10 is size if bus bar usually available is the
market.
so we can use 40x10sqmm copper busbar per phase for 630A.
for TPN- (3.5)x40x10
| Is This Answer Correct ? | 40 Yes | 7 No |
can you give any example at any parameters?
| Is This Answer Correct ? | 62 Yes | 37 No |
Answer / md.mahmudul hasan
we need to consider short ckt(KA) also. Say short ckt level
is 20KA then we need to select busbar accordingly.
| Is This Answer Correct ? | 30 Yes | 5 No |
I hv a question regarding power factor improvement just after transformer. I request you to reply me plzz. thank you sir. My friend has a small unit of fabrication. in his factory the main load is a welding machine, lathe machine, grinding machine. this load is not continuous type. now our electricity board has installed 16 KVA, 11000/433 V transformer for our factory. In the energy meter (trivector meter) at LV side of transformer, i hv seen power factor value of 0.15 only when only 3 KW load was flowing. Further electricity board has suggested to install 4 KVAR capacitor at LV side after energy meter. Now my question is that if we permanantly install and switch on 4 KVAR capacitor after energy meter, during some load on transformer and also without any load on transformer, wht will be the power factor shown in energy meter?i dont want to get any penalty by electricity board, so plz suggest me if i can permanantly install and switch on the 4 kvar capacitor or not at LV side of transformer just after energy meter? Thank you again and awaiting for ur positive reply soon.
Which supply is using for train AC or DC & what is the voltage????????
i have a wire.and the current flowing in that.when we cut the wire then why dont we seen the elactrons....
(In MEP services) HVAC in AC Plant room what else can we provide if the chiller is not considered?
IF HT CAPACITOR IN ON POSITION IS THERE ANY LOSSES I.S I SQURE OCCURS IN THE SYSTEM
What types of testing in 11Kv Ht switchgeat during testing?
What is the diff. between single compression and double compression gland
what is the difference between effective earthing and resistive earthing?
how many minutes or seconds taken by the transmission of electrical power from generating end to distributing end?
What is the formula to find out two phase active & reactive power
how we select the mva rating of the circuit breakers?
What are the possible causes if load is not same on all the three phases
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)