What is the meaning of burden and class of accuracy of CT?
Answer / poorvalingam
1.Burden is the actual load can handle by the C.T in (KVA)
Eg: the C.T need to operate the relay for fault tripping if the relay has 12 Va means the C.T burden must be greater than the relay load to over come the cable loss. it may be 15 va C.T enough
2.Accuracy class means , it says the % Errorof the C.T from no load to 120% of load for metering purpose and above the full load current for Protection C.T
| Is This Answer Correct ? | 2 Yes | 0 No |
What is LT Breaker Panel?
How to work E.L.C.B and how to connect in circuit.
Zone of protection and tripping scheme of arc protection relay.
WHAT IS THE DIFFERENCE B/W THREE POINT STARTER AND FOUR POINT STARTER
Do power transformers have an Automatic Voltage Regulator (AVR) just like the alternator/generator in a power system?
wht is an AVO metre. and whre it is used?
what is kondo syatem in eletrical traction
What is mean by CT Saturate? how do we calculate?
How to increase solar cell efficiency ?
what is the constructional difference between a power transformer and potentian transformer?
two bulbs of 100w and 40w respectively connected in paralel across a 230v supply.which bulb will glow bright and why?
HOW WOULD YOU PRESENT THE POWER FACTOR PRACTICALLY ON A GRAPH
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)