what is the working of air drayar
Answer / pillay
I believe you are talking about the air drier of a transformer
because this is an electrical forum.
When the transformer gets hot the insulating oil gets expended
and the air inside the conservator tank is pushed out through
the breather pipes and when the transformer gets cooler the
oil contracts and external air is drawn in. A path is created
for the movement of the air and some drying agent is placed
within them like silica gel.So all moisture is trapped by
drier.
| Is This Answer Correct ? | 1 Yes | 0 No |
What is STEP VOLTAGE ?
What is the function of earthfault relay?
18 Answers MultiTech, Tech Mahindra,
when transformer in load condition neutral earth testing wheater we can do it or not
What are the advantages of speed control using thyristor?
can we use IGBT as a AC-DC converting device in the applications?
In response to Mr Bikas. If fault current is 52 kA then what will be the CT specification
hi can any body send me syllabus of rrb electrical section engg... and past pepar also of any board...
Will any motor burn if voltage provided is lesser than the rated voltage???? If yes, then how is speed control possible with voltage control
What is Chatoliq Protection ?
On load tap changer (OLTC) explode? Transformer Vector group: Ynd11 Rated Power: 353MVA Rated Current: 693A Voltage:294/20KV OLTC Type: T III Y1000 110/c 12193w Max Operation Current: 295A Step Voltage: 550V Arrangement in Tx windings: Y Connection Problem: Damage of Unit 1 Generator Transformer On Load Tap Changer (OLTC) Description of Incident: 9.00 a.m. :- Generator No Load test on excitation system started 10.30 a.m :- Carried out AVR change over test 11.30 a.m :- Preparation for Generator Manual Synchronizing test 12.00 a.m :- Manual Synshronizing test started. Observed incoming generator voltage higher than running voltage. CECR operator operated Generator Transformer OLTC to bring down the incoming generator voltage 12.03 a.m :-Generator Transformer abnormal alarm operated at Gen.Control Desk (CECR) CECR operater at Generator transformer bay informed that the transformer oil splashed out from OLTC. CECR operater informed that he heard explosion inside OLTC. Observed Oil level & Oil Flow alaram operated at Tranformer local annunciator. 12.05 am :- CECR operator 'Open Gen Field Breaker” 12.10 a.m. :- Elec1 team inspected the OLTC and found the OLTC rupture disk was broken and oil spilled at OLTC area. - Elec1 found the OLTC top cover bulging. Do anyone know why and possibility cause happen in this OLTC.
what is meant by frequency ?
Cummins 750 KVA generator how much disel consumed per hour and how many units generated on 100% full load.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)