Answer / abdul rahman
Required capacitor KVAR :- KW X [tan cos (inverse(power factor old = 0.8)))-tan cos (inverse (power factor new = 0.9]
KVAR :- 15(TAN(C0S INVERSE (0.8)-TAN(COS(INVERSE (0.9))
= 15(TAN 36.86-TAN 25.84)
= 15(.75-.48)
= 15(.265)
= 4 KVAR
| Is This Answer Correct ? | 6 Yes | 0 No |
Using formula KVA^2= KW^2 + KVAr^2 ,find the values KVAr at 0.8 and 0.9 pfs. The difference is the required KVAr of the capacitor
| Is This Answer Correct ? | 4 Yes | 5 No |
hai...... tis is Hemanth. jst now completed electrical engineering... i wanna to apper for ap tranco exam... plzz send me the previous q's paper link......thanx in advance.
i have 2kv ups how many watts batteries is required
What is meant by cold loop test in instrument
acsr dog conductor specification
Briefly describe means used by electricity suppliers to influence the flow of active and reactive power in power networks (one for each type)?
What is different between DOL(Direct on line starter), VSD, S/S(Soft starter), and A/T(Auto Transformer)
hopkinson's test
what is working parincipal of a ht transformer
explain Xmer
a 25kvar capacitor bank connected to the secondary side of transformer.then why the capacitor draws more current then rated
How I design capacitor bank for different load.7MW connected load.
Which is remain unchanged in transformer action?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)