What is the Different b\w Circuit Breaker & Isolater
Answers were Sorted based on User's Feedback
Answer / e venkat reddy
CIRCUIT BREAKER WORKS ON ON LOAD WHERE AS ISOLATOR WORKS ON
OFF LOAD CONDITIONS. ISOLATOR WILL OPERATE AFTER THE
CIRCUIT BREAKER ACTION TAKING PLACE.
| Is This Answer Correct ? | 21 Yes | 1 No |
Answer / r.kalyana sundaram
IN CIRCUIT BREAKER THERE WILL BE TRIPPING MACHANISM.IN
ISOLATOR THERE WILL BE NO TRIPPING MECHANISM.ONLY ON,OFF
SWITCH FUCTION.
| Is This Answer Correct ? | 20 Yes | 0 No |
Answer / syed qamar abbas
Circuit Breaker is a automatic device while isolator
operates manually
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / mick
A circuit breaker is designed to automtically open the live
line if the current exceeds its rating - i.e. a 5A circuit
breaker will open and disconnect the live line should the
current exceed 5A. It primary purpose is to automtically
disconnect the live under a fault.
A isolator is usaully a hand operated device that will
disconnect the live and the neutral. Manly used to allow
work to be carried out on equipment (a motor for example).
Normally an isolator will have some way of being 'locked
off' so that the equipment cannot be energised. It does not
have an automatic function.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / rajesh ku sahu
# 2 CIRCUIT BREAKER WORKS ON ON LOAD WHERE AS ISOLATOR
WORKS ON
OFF LOAD CONDITIONS. ISOLATOR WILL OPERATE AFTER THE
CIRCUIT BREAKER ACTION TAKING PLACE.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / naresh kumar dhal
we can operate the isolator only manually.
But we can operate the cb Automatically with the help of a
relay and manually also
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / suthan prabhu
Isolator is an off line usable device.That means we are
using it for maintenance purpose.But Circuit breaker is a
switching device to use in On line .
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / nikesh
Circuit breaker is switch which operate manually during no load condition and operate automatically during fault condition or Isolater is operate off load condition after operate circuit breaker.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / chiranjit mondal
circuit breaker operates on load condition i.e it can break
inductive or capacitive current but isolator operates at no
current condition i.e itoperates when no current is flowing
through it.
| Is This Answer Correct ? | 2 Yes | 3 No |
what is counter poise conductors
How to discharge the battery as quickly as possible ?
What is the exact load current needed for a place which has 100nos of bulb of each 100w?
Why reverse power relay is used?
can a 150 kva 3 phase 440v/230V delta-wye step down transformer can be use as step up transfoermer with connected loads at 440v side?
Are same transformer be employed for step up and step down services?
what is LT & HT?
What is the IS standard for MCCB to be use (As per capacity of AMP)& for ACB also.
what is ideal insulator. what are its parameter. Is poecelain insulator comes under this category.
How do you commission a power Transformer?
Application wise, where we should use AC motors and where we should DC motors?
What is proportional controller?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)