I have two power supply.a)govt. power b)Captive power.3
phase load connected inside factory.when source change govt.
source to captive some motor rotate reverse. Is phase
sequence changes when if off & on?If I off generator & on it
again is it possible to get changed phase sequence??
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
The phase sequence does not change if you switch on and off
the captive power. Interchange two leads of the captive power.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / ganesh.a
no phase change will accur if u turn it off nad on again.check
the polarity of captive power
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ali raza
yas u can change the phase sequence from main supply any one (govt. or captive) then your motor rotate in one direction at both supply in our plant also same condetion happend then we change the phase sequencein generator terminal
Is This Answer Correct ? | 0 Yes | 1 No |
why rating of generator is kva but motor is kw ?
Why a starter is used for a motor?
50 Answers L&T, Nilachal Polytechnic,
How the value of KVAR of capacitor bank used in switchgears calculated??
Does human body can effect the electric shock when stand on Insulated material?
Grid fault level [KA]?
How to decide CT & PT ratings for a given transmission line carrying some rated voltage?
What is double throw isolator and single throw Isolator.
funtion of choke
In a Tap changing transformer where is the tap connected , is it connected in the primary side or it is connected in secondary side
What is the difference between diesel generator engine with and without turbo charger with the same capacity?
What will happen if i connect two 3-phase tranformers secondary supply on one bus bar that is R-Y-B-N?
WE HAVE A LOAD OF 55KW MOTOR ITS VOLTS 380 3PH AND ITS TAKING 100AMPS (ITS FULL LOAD IS 105AMPS)AND ITS CABLE IS 4CX50SQMM ,NOW ITS GETTING ABNORMAL HEATUP IN CABLE,PLZ TELL WHY ITS HEAT-UP?(CABLE LENGTH IS 15 METERS ONLY)