what is ISF
Answer / pradeep vaish
Instrument Security Factor is the ratio of Instrument Limit
Primary Current to the rated Primary Current. Instrument
Limit Current of a metering Current Transformer is the
maximum value of primary current beyond which Current
Transformer core becomes saturated. Instrument Security
Factor of CT is the significant factor for choosing the
metering Instruments which to be connected to the secondary
of the CT. Security or Safety of the measuring unit is
better, if ISF is low
| Is This Answer Correct ? | 0 Yes | 0 No |
Tell me the reason of connecting domestic t/f primary in star or delta,and also secondary side.
Why CT secondary should not left open??????????
132/66kv sub-station procation ?
What is the minimum distance to be maintained in between HT panel and LT panel and Instrument panel as per IEC and NEC standards?
What Should be the rating of transformer used in 33KV substation?
How to measure the Harmonic Distortion of UPS ie THD?
what is the dedicated neutral earth in ups? y its required?
what is power transformer?
What is the formula to find out the kvar required to improve the powerfactor from .85 to .99 at 1500kw, 415v.
What is current & voltage ? Voltage perform at any load without current or not?
HOW TO CALCULATE CT AND VT RATIO IN PRTECTION AND METERING?
1 Answers College School Exams Tests, L&T,
why does connected a indutor with mnsformeretering core of current transformer ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)