What should be value of Circuit breaker operating time and
tripping time?
Answers were Sorted based on User's Feedback
Answer / alpglk
Typical Operating times for HV/EHV/UHV Circuit Breakers
Tripping/Opening: 25-40ms
Closing: 80-140ms
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / sreekanth bammidi
Generally the operating time of the circuit breakers
depends on the designer. The opening time of the breaker
should be less than the closing of the breaker. Opening
time should be less than or equal to 20msec (preferrable).
Closing time depends but preferrably less than 90msec.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / arun
Circuit breaker closing tome 60 msec
triping time lessthan 40msec
| Is This Answer Correct ? | 8 Yes | 9 No |
Answer / vijay mali
Generally the operating time of the circuit breakers
depends on the designer. The opening time of the breaker
should be less than the closing of the breaker. Opening
time should be less than or equal to 20msec (preferrable).
Closing time depends but preferrably less than 90msec
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / rajesh kumar
circuit breaker closing time 40msec.
circuit breaker tripping time less than 20 msec.
| Is This Answer Correct ? | 4 Yes | 8 No |
What is the basic difference of turn ratio & transformation ratio for a transformer?
On the secondary side of a distribution transformer, we use 1c x 630 sq mm cable. Why dont we use 4 core cables instead of 1 core cables on the secondary. Why we use aluminium cable glands on the outgoing instead of brass cable glands?
why transformer ratings in kva? & DG ratings in kva? & Motor ratings in kw/HP?
Can I use RCCB in moisture control device in a submersible pump.
how can H.V busbar in a powerstation can be protected?
What device is use for metering current at lt consumer end..??
I have a situation to design sub-Distribution board/Panel meant for feeding power sockets. In the incomer CAN i Take TP MCCB with Neutral Link and All the outgoing feeders with to sockets with TP MCCB and Neutral Link? P.S : My System is IT Earthing
What is the kiosk parts, about them and their functions ? If anybody have some PDFs files or details about this plz send it on tawhidfaisal@Yahoo.com
Why infinite busbar has zero resistance and high mechanical inertia?
what is AB switch???
What are the special protection given for high capacity Motor, more then 10mw
1 hp single phase motor is more likely to get hot thsn inone hp 3 phase motor its true or false? If true why?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)