what is ISF

Answer Posted / pradeep vaish

Instrument Security Factor is the ratio of Instrument Limit
Primary Current to the rated Primary Current. Instrument
Limit Current of a metering Current Transformer is the
maximum value of primary current beyond which Current
Transformer core becomes saturated. Instrument Security
Factor of CT is the significant factor for choosing the
metering Instruments which to be connected to the secondary
of the CT. Security or Safety of the measuring unit is
better, if ISF is low

Is This Answer Correct ?    0 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

Please explain the following and how these are working with PLC unit 1.I/O Module 2.I/O Device 3.Adaptor Card 4.Ribbon Adaptor 5.RS 485-FC

1171


In radial network the source is fed from 1 end both ends at central

1609


Why magnetic flux produces an induced current?? what is the detailed procedure ?? ans plz

3226


what is differnce btwen lll and lllg faults

1507


What is vacuum circuit breaker.define with cause and where be use it device?

722






what is gridrotor resistance starter

1434


what is parellel power factor correction?

3418


What should be setting for alarm,tripping and cooling fan on for power transformer's oil temp. and winding temp. indicator?

1448


WHAT IS THE WINDING PROCEDURE OF ELECTRICAL MOTOR

3520


If a rotary UPS is in line through grid power; What would be the impact on Power Factor if the load through rotary ups is 25% , 50% , 75% & 100%. Will the power factor reduce with less load?

1416


What are the basic components of the feedback control system?

614


how many load we can take for lighting

1747


What is kvar?

851


33kv substation lay out details & line to line & line to earth measurements

2160


What is voltage ratio of a transformer?

630