What is the minimum load that you can keep in a 3 Phase 40
KVA Diesel Generator? Is it neccessary to load all the 3
phases? Can a phase be left without load?
Answers were Sorted based on User's Feedback
Answer / binod barik
3PH 40KVA IS THE O/P OF THE GENERATOR MAX.LOAD WE RECEIVE
IS=40*.8=32KW( TAKING STD. AS COS IS 0.8 OF THELOAD SIDE
POWER FACTOR).TAKING MIN. LOAD MEANS DECREASING ITS
EFFICIENCY. YES IT IS NECESSARY TO GIVE BLANCE LOAD IN 3
PH SIDE TO AVOID HEATING & TO GET MAX EFFICIENCY, SO NO
PHASE LEFT WITHOUT LOAD
| Is This Answer Correct ? | 4 Yes | 2 No |
what is elcb
What are the drawbacks of HVDC system?
Explain why the Voltage drop will happen in 3 Phase line?
How the electric train gets the supply of electricity? What is the return path of the current?
What are the material used for resistor?
why selected genration, transmission or any at 11kv, 132, 220, 220 or 440 voltage which is propotional to 11. why does not any for ex. 12 kv 13kv or any
differentional compound gernater used for wielding porpose. why????????//
Utility company give the supply to customer in KVA but bill them for Watt.why?
expansion of rccb
In Slip ring Induction Motor we use Liquid Rotor Starter for Starter Every Time Liquid Filling we need add Soda Sodium Carbonate or only Distilled water is Enough.
Current Transformer's star point must face the protected object for the relay operation?
difrent between vcb acb sf6 and mccb breakers
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)