in GEAFOL Cast-Resin trnaformer of 11/.72kv which has
tapping of 11550v,11250,11000,10246v in primary side. To
obtain 700v. which tapping should be used of HV side as we
have 11000v/720v tapping now .
If the primary voltage [supplied by Utility] it is NOW 11
kV and your transformer at no-load shows 720 V at its
secondary terminals the ratio primary/secondary voltage is
11/0.72=15.278. If you want to reduce the secondary to 700
V you have to change the ratio to 11/0.7=15.714.
Let's say the rated secondary voltage [at no-load] is 720 V.
That means the ratio 11250/720=15.625 it is the most
suitable and you'll get 11000/15.625=704 V at secondary
terminal [at no-load].
| Is This Answer Correct ? | 1 Yes | 0 No |
what is the difference between a race around condition and toggling?
Which motor will you choose which can operate in both lagging as well as leading power factors?
What is double delta conection in AC Motor? And can we done the double RPM of the motor by double delta conection?
What is the function of PMG in DG sets & how it works??????????
WHAT IS OLTC OF TRANSFORMER? WHERE IS ITS USED EITHER ON PRIMARY OR SECONDARY SIDE OF TRANSFORMER?
If the capacitor bank is installed in switchyard say 132/22kv then on LT side say 22kv/0.433kv is it necessary to install capacitor bank for maintaining power factor. if pf is maintained on HT side then will that be maintained on LT side as well.if not then how&why??????/ please explain...........
how i prepare for the written test in mahagenco?
2 Answers MahaDiscom, MahaGenco, Wipro,
why the starting voltage drop in a cable needs to be limited?what is percentage of the voltage drop allowed during starting?
We have a 12MW power plant & we inject 5-6MW power to Orissa GRID. For this we have a 33KV/11KV switch yard having 12.5MVA power transformer. Some times we draw power during emergency. It is observed that during Export or Import for load less than 500Kw the power factor is decreasing to 0.3 . This is happening only during export or import. During island condition TG power factor OK.Our capacitor bank is provided with our Power plant auxilliary load. Please suggest how I can we improve our power factor during low load (GRID).
What is difference b/w fuse and breaker?
Even when a particular generator in a generating station is under maintenance we are still able to maintain the same power output. How is this possible? Does the tie line between 2 generating stations have a role to play in it?
why ac supply neutral should earth not in dc (-)
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)