What is difference b/w fuse and breaker?
Answers were Sorted based on User's Feedback
Answer / nasir.ansari888
Fuses are burned at time of over current flows in the ckt but breaker are just open at the time of over current flows.
| Is This Answer Correct ? | 24 Yes | 2 No |
Both are protective devices.Fuses are cannot reuse,but the breaker can reuse.breaker can use for any voltage but fuses used only in the limited voltage only.
| Is This Answer Correct ? | 9 Yes | 0 No |
Answer / chreamz
A fuse is a normally closed protective device that ionises
(burnout open circuitry) under fault condition or when
current over its rating flow through it. Everything happens
automatically with no external actuator. Once blown, it
must be replaced. A circuit breaker if also a protective
device that gets a closing/tripping command from the relay.
It has internal & external devices (actuator) that bring
about execute the action sent by the relay. The life span
of the CB depends on the load, operation and maintenance.
| Is This Answer Correct ? | 6 Yes | 0 No |
What is the LUX
how much watts are equal to one unit of energy meter?
Why are the voltage levels in a powersystem are 11KV,33KV etc., why not 10KV,30KV?
i have 2kv ups how many watts batteries is required
What are the loading factors to be considered for transformer sizing/selection?
ASTM D 3455 - Standard Test Methods for Compatibility of Construction Material with Electrical Insulating Oil of Petroleum Origin has been used for Testing Transformer Oils with a product placed in it. Aged Control Oil has a Power Factor of 0.032% at 100°C. Aged Oil with a Test component has a Power Factor of 0.093% at 100°. Is this increase acceptable? If not why? How much increase is acceptable?
what is the back ground of transformer working? applying voltage to primary and emf inducing in primary and secondary? how it is possible? please answer me with scientific approach?
If breaker is undefined position, first step to do.
How much should be the specific gravity of a DG set battery Electrolyte.
Why we are using LA Rating 10kA in 66 kv substation
If my sfu is 64 Amp & its link is 32 Amp then at what amp.my sfu will trip???
what are the functions of power modulator?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)