If the capacitor bank is installed in switchyard say
132/22kv then on LT side say 22kv/0.433kv is it necessary to
install capacitor bank for maintaining power factor. if pf
is maintained on HT side then will that be maintained on LT
side as well.if not then how&why??????/ please
explain...........
Answers were Sorted based on User's Feedback
Answer / vijaykumarht
The capacitor bank on HT side will anyhow correct the PF,
the line losses will not be reduced. hence by putting the
capacitors on LT side, that too nearer to the load, the
losses and PF can be much better improved. The capacitors on
HT side is just to minimize the line losses, even though it
improves PF putting capacitors on LT side is always
recommended that too nearer to load, so as to get efficient
usage of electricity.
Please not that this answer is only for inductive load
consideration as linelosses and transformers and most of the
loads conneted to the line is inductive.
| Is This Answer Correct ? | 23 Yes | 1 No |
Answer / zahid noor
If capacitor bank is installed in switchyard & capacitors
are connected on HT side , it will try to balance losses of
transmission line and not towards LT side, where as for
maintaining /increasing LT side voltage, we need to install
seperate capacitors nearer to load so as to maintain PF at
LT side also depending upon connected load & distance of
equipment connected in LT side.
| Is This Answer Correct ? | 12 Yes | 0 No |
Answer / kola raju
If the capacitors are installed in the ht side the pf of
the line improves but not the plant.And the plant pf is in
poor condition only which may leads to the losses on our
side and reactive load on the transformer may increase so
even if we have capacitors on ht side it is advaisable to
kept the capacitors on load side also.
| Is This Answer Correct ? | 9 Yes | 3 No |
How many types of faults are there in 3 phase power system?
How to find the length of a Xlpe cable required to transmit 3mva load at 22kv.
What is BKW of Motor. And what its significance
why transformer fuse wire is very thin as compared to home fuse wire while voltage lavel is low
. Draw the vector diagram and condition for the following: 1) Dyn1 2) Ynd0 3) YnYn0
sir, 3phase induction motor takes different pf and different KW in three phase while running,explain reason
what is mean by xlpe swa pvc
We are using 4 MVA transformer and we provided 2 separate earthing pit for Body and 2 separate earthing pit for neutral, can we connect separate body earthing pit to other earthing pit (Equipment earthing)?
What will be the direction of rotation of a Alternator in case it goes in motoring action when connected with grid ?
why are transformer rating in MVA
How to create a SCADA diagram on PC? I run the DG everyday but i dont know how that animated single line diagram is created.Please answer.
why open-delta core of 11kv Potential Transformer is 11000v/1.732/110/3?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)