We have a 12MW power plant & we inject 5-6MW power to
Orissa GRID. For this we have a 33KV/11KV switch yard
having 12.5MVA power transformer. Some times we draw power
during emergency. It is observed that during Export or
Import for load less than 500Kw the power factor is
decreasing to 0.3 . This is happening only during export or
import. During island condition TG power factor OK.Our
capacitor bank is provided with our Power plant auxilliary
load. Please suggest how I can we improve our power factor
during low load (GRID).
Answers were Sorted based on User's Feedback
Answer / velusamy
This problem can be solved by switching off all capacitor
banks during low load. we have faced Similar type of
problem in our cement plant loads which are fluctuating in
nature which causes export / import of power fluctuation(
loads go +500kw and - 500kw withing 1 or two seconds).
The main reason for this low power factor is due to
reactive power consumption of your 12.5 MVA power
transformer.
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / s.balasubramanian
If you can furnish me the scheme used by you for import
export ontrol I will be able to review
balasubramanian
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
During export, it may be possible to improve pf with
excitation.The low pf may also be attributed to erroneous
measurement by CT's at very low loads.Tr may also contribute
to low pf to some extent depending on positions of pf meter
and capacitor bank .
| Is This Answer Correct ? | 0 Yes | 0 No |
which course is maximum demand in industry and give me the list of best courses for electrical engineers
which one is dangerous AC Power r DC Power for Electrical Shock ?
In Battery Charger - What is the meaning of End Cell Voltage and Float Voltage.
9 Answers FLSmidth, Focus, PSEB,
which generator is called as brushless excitation generator and why??
What accessories required to give the motor with given circuits and do you know the ratings of those accessories?
which calss ct's,pt', use protection,meatering and others
Does dry and oil transformers both require dedicated neutral, because in my project we are using 2500kv dry star delta transformer, where they say neutral not required and even it is not provided in our substation. can u let me know
Why increase in current leads to increase in conductor temperature?
what is meant by carrier aided trip protection in transmission line
dear friends plz send link about reluctance & universal motor .thank u
What is the max demand on your transformer and your company?
10 Answers Bhel, CBRE, Core Consultants, HPL, IOCL, JLL, L&T, Lemon Tree, MNC, Rashmi, TATA, Tata Motors, Tata Power, Torrent Pharma,
How does a system control centre in a utility plant gets the grid frequency of the electrical network (50 Hz or 60 Hz)by the SCADA system?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)