We have a 12MW power plant & we inject 5-6MW power to
Orissa GRID. For this we have a 33KV/11KV switch yard
having 12.5MVA power transformer. Some times we draw power
during emergency. It is observed that during Export or
Import for load less than 500Kw the power factor is
decreasing to 0.3 . This is happening only during export or
import. During island condition TG power factor OK.Our
capacitor bank is provided with our Power plant auxilliary
load. Please suggest how I can we improve our power factor
during low load (GRID).
Answers were Sorted based on User's Feedback
Answer / velusamy
This problem can be solved by switching off all capacitor
banks during low load. we have faced Similar type of
problem in our cement plant loads which are fluctuating in
nature which causes export / import of power fluctuation(
loads go +500kw and - 500kw withing 1 or two seconds).
The main reason for this low power factor is due to
reactive power consumption of your 12.5 MVA power
transformer.
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / s.balasubramanian
If you can furnish me the scheme used by you for import
export ontrol I will be able to review
balasubramanian
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
During export, it may be possible to improve pf with
excitation.The low pf may also be attributed to erroneous
measurement by CT's at very low loads.Tr may also contribute
to low pf to some extent depending on positions of pf meter
and capacitor bank .
| Is This Answer Correct ? | 0 Yes | 0 No |
what factors to needed while selecting a MCB and MCCB
why does a dc machine has high efficiency while working as a generator than as a motor ..
3 ph motor connected in star delta starter. when we start the motor it run in star but when in is going in delta it trips the main incoming supply. why?
why we measure output of transformer in kva?
Is it possible we are step down 11 kv to 230v ?
How to measure current and voltage in an ELV circuit
I have 320 Kva DG Set his KWh running is 77 , how i can calculate into electrical unit .
2 Answers Anuj Enterprises, Schneider,
What is done to avoid interference of high frequency transmission lines with communication lines??
i want to know about torque of slip ring induction motor
what will happen power cables laid without gap in underground
what do you mean by synchronous speed of a three phase induction motor?
What is communication? What are the different stagesin the communication process?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)