Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


We have a 12MW power plant & we inject 5-6MW power to
Orissa GRID. For this we have a 33KV/11KV switch yard
having 12.5MVA power transformer. Some times we draw power
during emergency. It is observed that during Export or
Import for load less than 500Kw the power factor is
decreasing to 0.3 . This is happening only during export or
import. During island condition TG power factor OK.Our
capacitor bank is provided with our Power plant auxilliary
load. Please suggest how I can we improve our power factor
during low load (GRID).

Answers were Sorted based on User's Feedback



We have a 12MW power plant & we inject 5-6MW power to Orissa GRID. For this we have a 33KV/11K..

Answer / velusamy

This problem can be solved by switching off all capacitor
banks during low load. we have faced Similar type of
problem in our cement plant loads which are fluctuating in
nature which causes export / import of power fluctuation(
loads go +500kw and - 500kw withing 1 or two seconds).

The main reason for this low power factor is due to
reactive power consumption of your 12.5 MVA power
transformer.

Is This Answer Correct ?    2 Yes 2 No

We have a 12MW power plant & we inject 5-6MW power to Orissa GRID. For this we have a 33KV/11K..

Answer / s.balasubramanian

If you can furnish me the scheme used by you for import
export ontrol I will be able to review
balasubramanian

Is This Answer Correct ?    0 Yes 0 No

We have a 12MW power plant & we inject 5-6MW power to Orissa GRID. For this we have a 33KV/11K..

Answer / k.prakashchandra

During export, it may be possible to improve pf with
excitation.The low pf may also be attributed to erroneous
measurement by CT's at very low loads.Tr may also contribute
to low pf to some extent depending on positions of pf meter
and capacitor bank .

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

what is d main difference between KVA and KWA

2 Answers   Charoen Pokphand,


Induction motor & transformer both has magnetic core,then why induction motor is a inductive load & transformer not???

6 Answers   SBL,


What is the current flow in 230v ac supply ? What is the current flow in 415v Ac supply ?

6 Answers  


what is the relation between currebt & voltage.

8 Answers  


what is the difference between switchgear and circuit breakers and is there any difference between outdoor and indoor switchgear and circuit breakers , and how would you differentiate between switch yard and substation and grid station . thanks

0 Answers   ABC,


A 100KVA SINGLE PHASE TRANSFORMER 10000/200V,50HZ REQUIRES 300V AT HV SIDE TO CIRCULATE FULL LOAD CURRENT WITH LV SHORT CIRCUITED.THE INTAKE IS 1000W.THE % OF REGULATION ON FULL LOAD AT 0.8 PF LAGGING WILL BE HOW MUCH AND THE SECONDARY TERMINAL VOLTAGE ON 0.8 PF LEADING WILL BE

0 Answers   IAS, TATA,


What is Black-out and Brown-out situation in the context of voltage stability in power system?

1 Answers  


What loads the lagging and leading effects comes in a circuit?

5 Answers  


can i able to get bhel previous exam question paper?

0 Answers   Bhel,


what is the different between RCCB & ELCB

3 Answers  


n1 =1000 n2 =?;v1 =200:v2 =400

1 Answers   APGenco,


How power cable & control cable can be differentiate from each other ?explain?

14 Answers   Aster, Finolex, TCE,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)