We have a 12MW power plant & we inject 5-6MW power to
Orissa GRID. For this we have a 33KV/11KV switch yard
having 12.5MVA power transformer. Some times we draw power
during emergency. It is observed that during Export or
Import for load less than 500Kw the power factor is
decreasing to 0.3 . This is happening only during export or
import. During island condition TG power factor OK.Our
capacitor bank is provided with our Power plant auxilliary
load. Please suggest how I can we improve our power factor
during low load (GRID).
Answers were Sorted based on User's Feedback
Answer / velusamy
This problem can be solved by switching off all capacitor
banks during low load. we have faced Similar type of
problem in our cement plant loads which are fluctuating in
nature which causes export / import of power fluctuation(
loads go +500kw and - 500kw withing 1 or two seconds).
The main reason for this low power factor is due to
reactive power consumption of your 12.5 MVA power
transformer.
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / s.balasubramanian
If you can furnish me the scheme used by you for import
export ontrol I will be able to review
balasubramanian
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
During export, it may be possible to improve pf with
excitation.The low pf may also be attributed to erroneous
measurement by CT's at very low loads.Tr may also contribute
to low pf to some extent depending on positions of pf meter
and capacitor bank .
Is This Answer Correct ? | 0 Yes | 0 No |
why zero sequence impedance measurement is not applicable for single phase GT
Power Factor Correction Panel (Manual & Automatic)
Why we are going for converter transformers for DC drives application instead of distribution transformer?
Brushes are placed at magnetically neutral axis,when brushes reach that point,the armature conductor gets shorted,but it can be seen that the dc supply is also shorted,wont that get damage? help me plz
What happens to the terminal voltage of an alternator connected to a bus bar when it is suddenly disconnected from the bus bar??
while calculating demand in my company the present load in kw is 212.... there 125kvar capacitor bank is installed by spliting as 50 in departments...the diasplay in panek biard shows 175kw... how could we know the amount of kvar used to compensate the kva
What is In (current rating) shown on the MCCB? Is this full load which can withstand by the circuit breaker
how to reduce the initial starting amps which is equal to the running load amps
why the vfd motor take current high in vfd panel then mcc panel.current in vfd panel=160A in 93%.and mcc panel it shows 130A. (132kw motor)
What is system earthing?what are the types?
single phase brower fan with control starter. *problem is when operate it.It will be trip.
plzzzzzzzzz plzz send me the papers of JSPL WRITTEN TEST..SO that i can prepare for the test in electrical engg..