We have a 12MW power plant & we inject 5-6MW power to
Orissa GRID. For this we have a 33KV/11KV switch yard
having 12.5MVA power transformer. Some times we draw power
during emergency. It is observed that during Export or
Import for load less than 500Kw the power factor is
decreasing to 0.3 . This is happening only during export or
import. During island condition TG power factor OK.Our
capacitor bank is provided with our Power plant auxilliary
load. Please suggest how I can we improve our power factor
during low load (GRID).
Answers were Sorted based on User's Feedback
Answer / velusamy
This problem can be solved by switching off all capacitor
banks during low load. we have faced Similar type of
problem in our cement plant loads which are fluctuating in
nature which causes export / import of power fluctuation(
loads go +500kw and - 500kw withing 1 or two seconds).
The main reason for this low power factor is due to
reactive power consumption of your 12.5 MVA power
transformer.
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / s.balasubramanian
If you can furnish me the scheme used by you for import
export ontrol I will be able to review
balasubramanian
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
During export, it may be possible to improve pf with
excitation.The low pf may also be attributed to erroneous
measurement by CT's at very low loads.Tr may also contribute
to low pf to some extent depending on positions of pf meter
and capacitor bank .
| Is This Answer Correct ? | 0 Yes | 0 No |
why in some cases the receiving end voltage is higher than the sending end voltage in transmission line (called 'Ferranti effect') ????? whts the reason behind tht???
what is the question paper model for section engineer in RRB
In step down transformer (415/200V),mistakenly secondary side is connected to 415V for some hours, what would be result of this condition?
19 Answers Essar, GAIL, Vizag Steel,
how the alternator transfere mechanical energy to electrical one ??
What is the formula for finding fault level of generator?
What is difference between SMC supportg and Glass Fibre Reinforced Plastic Support.
What is the basic diffrence between Electronics & Electrical engineering
how does the thyistor work in dc drive?
Dear sir please mera ye sawaal hai ki rccb ka kya kaam hota hai please answer hindi me dizyega dhanyya waad
How o select the electrical fuse?.What are its characteristics.How to select the material od fuse?
What are the Formula of computing Back up Time of 500kVA UPS with 4 Battery Banks, each bank composed of 43 pcs of Batteries 12V150Ah. How to compute the Back up Time of UPS? We have also 3X500kVA UPS running in Parallel same composition as I write above.
why lightning arrester and other equipment earthing conneting from same earth bar ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)