can we replace a pressure transmitter of range 0 to 25
Kg/cm2 by a Pressure transmitter of range 0 to 10
Kg/cm2 ?.. Will it affect 4 to 20 mA output signal which we
will feed to the PLC.
Answers were Sorted based on User's Feedback
Answer / ruchita
Yes it will affect the 4-20 mA signal. say for example if we are using PT of rsnge 0 to 25 bar bt internally we use only 0 to 10 bar range den it can be replaced otherwise not
| Is This Answer Correct ? | 9 Yes | 4 No |
Answer / yashwant
yes, only make sure the pressure will never rise beyond 10 I
think its design for 25 in safety condition. if u wish O/p in
0-10 you can scale 4-20 ma as 0-10 at plc, no need to change
tx.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / vijay
it depend upon ur range in the application for example
piston producing pressure within 10kg/cm2 then u can use it
by change program in the plc otherwise u cant
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / vinod hepat
Yes first of all note whether range is suitable for ur
application.replace transmitter & accordingly change the
range in DCS.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / madhav kamble
Yes. you can replace the pressure transmitter form 0-25 to
0-10. it willnot change the 4-20 mA which we will send to
the PLC but you to change the calibration at PLC for New
0-10 transmitter.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / govind singh
Going by standards, 20 mA of first transmitter will read 25 kg/cm2 pressure, while same reading for second transmitter will be 10 kg/cm2. So at same pressure, both transmitters will send different current signals. So calibration at the DCS end will be needed.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / imran
first of all you need permission to replace pressure tx
from operation instead 0-25 by swaping 0-10cause it will
effect process & may you r going to upset process other
point of view by technical you need to configure it & it
will give you output vice varsa
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / dinesh kumar
Its not possible by answering without knowing the application
But in both the cases v can get the 4-20mA output
In case if the o/p doesnt goes beyond 10kg then v can replace and the o/p side of tx shud be calibrated before installing and the changes shud be entered on plc.
In another case if the user wants better accuracy he may b using 0-25kg/cm2 tx eventhough the internal pressure is b/w 0-10kg/cm2
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / trideep
If range is in b/w 0-10 kg/cm2 or with in that, then it will do..
| Is This Answer Correct ? | 0 Yes | 3 No |
Using your own examples solve a problem involving normal table. (experimental method and analysis)
A temperature sensor (RTD) connected via a temperature transmitter is adjusted to give an output of 4ma at 60 deg and 20 ma at 600 deg. This output (4-20ma) from the transmitter is connected to an IGBT-inverter to control a high speed (-12,000 to +12,000 RPM) DC motor. And in the inverter it is programmed as, for 4ma the motor speed will be -3,000 RPM and for 20ma the motor speed will be +10,000 RPM. The question is : If the motor speed is +5,500 (RPM), what will be the temperature? (-sign indicates that the motion is in reverse direction).
in my company organisation in plan to take new PLC system for replacing old relay system , for that what I/P needsd to submit to the system house of PLC supplier?
what does it mean an active front end in vfd plz explain it briefly
what is the essential difference between DIODE and SCR in term of application.
whats the working principle of level transmeter?
what are procedure of sox-nox calibration
Actual using of tube bender to bend 2 opposite 90 deg at correct measurement center to center of tubing.
What is the reverse action and direct action
Before erect the instrument what should you do?
what is difference between HART communication and BRAIN communication?
what is meant by calibration
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)