can we replace a pressure transmitter of range 0 to 25
Kg/cm2 by a Pressure transmitter of range 0 to 10
Kg/cm2 ?.. Will it affect 4 to 20 mA output signal which we
will feed to the PLC.
Answers were Sorted based on User's Feedback
Answer / ruchita
Yes it will affect the 4-20 mA signal. say for example if we are using PT of rsnge 0 to 25 bar bt internally we use only 0 to 10 bar range den it can be replaced otherwise not
Is This Answer Correct ? | 9 Yes | 4 No |
Answer / yashwant
yes, only make sure the pressure will never rise beyond 10 I
think its design for 25 in safety condition. if u wish O/p in
0-10 you can scale 4-20 ma as 0-10 at plc, no need to change
tx.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / vijay
it depend upon ur range in the application for example
piston producing pressure within 10kg/cm2 then u can use it
by change program in the plc otherwise u cant
Is This Answer Correct ? | 5 Yes | 3 No |
Answer / vinod hepat
Yes first of all note whether range is suitable for ur
application.replace transmitter & accordingly change the
range in DCS.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / madhav kamble
Yes. you can replace the pressure transmitter form 0-25 to
0-10. it willnot change the 4-20 mA which we will send to
the PLC but you to change the calibration at PLC for New
0-10 transmitter.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / govind singh
Going by standards, 20 mA of first transmitter will read 25 kg/cm2 pressure, while same reading for second transmitter will be 10 kg/cm2. So at same pressure, both transmitters will send different current signals. So calibration at the DCS end will be needed.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / imran
first of all you need permission to replace pressure tx
from operation instead 0-25 by swaping 0-10cause it will
effect process & may you r going to upset process other
point of view by technical you need to configure it & it
will give you output vice varsa
Is This Answer Correct ? | 2 Yes | 3 No |
Answer / dinesh kumar
Its not possible by answering without knowing the application
But in both the cases v can get the 4-20mA output
In case if the o/p doesnt goes beyond 10kg then v can replace and the o/p side of tx shud be calibrated before installing and the changes shud be entered on plc.
In another case if the user wants better accuracy he may b using 0-25kg/cm2 tx eventhough the internal pressure is b/w 0-10kg/cm2
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / trideep
If range is in b/w 0-10 kg/cm2 or with in that, then it will do..
Is This Answer Correct ? | 0 Yes | 3 No |
Describe the function of Accumulator into the Pump
how can we measure the level measurement with the help of pressure gauge?
i want to measure temp of hot sand(welding flux) in closed chamber(around 150 deg C).Which is better thermocouple or thermometer?
What is critcal speed. what is resonant frequency. why we want to cross crtcal speed on higher RPM (early).
What is paid how it works
Why we are using temperature and pressure as a reference when measuring flow of steam?
Draw a complete P&ID of a flow suction tank indicating all control & protection equipment. Indicate all its inlets and outlets. Explain the controls for this system
What are the cable come out from the paddle type flow sensor.and how is further connections
what is the difference between AUTOMATION AND INSTRUMENTATION?
How does one detrmine the direction of movement of core in an LVDT?
Which boiler is use in power plant
what is the diffrence between LCN and UCN