Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


can we replace a pressure transmitter of range 0 to 25
Kg/cm2 by a Pressure transmitter of range 0 to 10
Kg/cm2 ?.. Will it affect 4 to 20 mA output signal which we
will feed to the PLC.

Answers were Sorted based on User's Feedback



can we replace a pressure transmitter of range 0 to 25 Kg/cm2 by a Pressure transmitter of range 0..

Answer / ruchita

Yes it will affect the 4-20 mA signal. say for example if we are using PT of rsnge 0 to 25 bar bt internally we use only 0 to 10 bar range den it can be replaced otherwise not

Is This Answer Correct ?    9 Yes 4 No

can we replace a pressure transmitter of range 0 to 25 Kg/cm2 by a Pressure transmitter of range 0..

Answer / yashwant

yes, only make sure the pressure will never rise beyond 10 I
think its design for 25 in safety condition. if u wish O/p in
0-10 you can scale 4-20 ma as 0-10 at plc, no need to change
tx.

Is This Answer Correct ?    5 Yes 0 No

can we replace a pressure transmitter of range 0 to 25 Kg/cm2 by a Pressure transmitter of range 0..

Answer / vijay

it depend upon ur range in the application for example
piston producing pressure within 10kg/cm2 then u can use it
by change program in the plc otherwise u cant

Is This Answer Correct ?    5 Yes 3 No

can we replace a pressure transmitter of range 0 to 25 Kg/cm2 by a Pressure transmitter of range 0..

Answer / vinod hepat

Yes first of all note whether range is suitable for ur
application.replace transmitter & accordingly change the
range in DCS.

Is This Answer Correct ?    2 Yes 0 No

can we replace a pressure transmitter of range 0 to 25 Kg/cm2 by a Pressure transmitter of range 0..

Answer / madhav kamble

Yes. you can replace the pressure transmitter form 0-25 to
0-10. it willnot change the 4-20 mA which we will send to
the PLC but you to change the calibration at PLC for New
0-10 transmitter.

Is This Answer Correct ?    2 Yes 1 No

can we replace a pressure transmitter of range 0 to 25 Kg/cm2 by a Pressure transmitter of range 0..

Answer / govind singh

Going by standards, 20 mA of first transmitter will read 25 kg/cm2 pressure, while same reading for second transmitter will be 10 kg/cm2. So at same pressure, both transmitters will send different current signals. So calibration at the DCS end will be needed.

Is This Answer Correct ?    1 Yes 0 No

can we replace a pressure transmitter of range 0 to 25 Kg/cm2 by a Pressure transmitter of range 0..

Answer / imran

first of all you need permission to replace pressure tx
from operation instead 0-25 by swaping 0-10cause it will
effect process & may you r going to upset process other
point of view by technical you need to configure it & it
will give you output vice varsa

Is This Answer Correct ?    2 Yes 3 No

can we replace a pressure transmitter of range 0 to 25 Kg/cm2 by a Pressure transmitter of range 0..

Answer / dinesh kumar

Its not possible by answering without knowing the application

But in both the cases v can get the 4-20mA output

In case if the o/p doesnt goes beyond 10kg then v can replace and the o/p side of tx shud be calibrated before installing and the changes shud be entered on plc.

In another case if the user wants better accuracy he may b using 0-25kg/cm2 tx eventhough the internal pressure is b/w 0-10kg/cm2

Is This Answer Correct ?    0 Yes 1 No

can we replace a pressure transmitter of range 0 to 25 Kg/cm2 by a Pressure transmitter of range 0..

Answer / trideep

If range is in b/w 0-10 kg/cm2 or with in that, then it will do..

Is This Answer Correct ?    0 Yes 3 No

Post New Answer

More Instrumentation Interview Questions

how to calculate density?

2 Answers  


how to install Differential pressure transmitter in gas line.i need transmitter down side.

7 Answers   Rockwell,


why flow transmitter showing 2.2ma?

2 Answers  


suppose there is gas flow meter I want to know weather meter calibration is done at high pressure or low pressure? pls justify.

2 Answers   Siemens,


What is the reason for not giving very High Proportional Gain Kp in PID Controller?

2 Answers   ABB,


GIVE THE TEMPERATURE RANGE OF PLATIUM RESISTANCE THERMOMETER.

7 Answers   DVC,


Using your own examples solve a problem involving normal table. (experimental method and analysis)

0 Answers  


line up procedure for dp type flow transmitter?

0 Answers  


What is Predictive Maintenance

0 Answers  


can anyone can let me know in Eurotron Micro cal 2+ calibrator in milli amps source mode we are not able to get 20 milli amps output it only produces 1.52 milli amps out, but display shows increase in milli amps , and err6 displays, let me know how to remove the err 6.

0 Answers  


i am having information technology branh ....... can i prepare for psu exam

0 Answers  


Why boiler chimney area  oxyden sensor fixing? 

0 Answers   NTPC,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)