For an 100kw generator, only 50kw of load is connected.
will the generator generate only 50kw or 100kw. if it
generate 100kw what happens to rest of the 50kw. what
happens if we connect more than 100kw of load?
Answers were Sorted based on User's Feedback
Answer / jaipal
If we connect only 50kw load to the 100kw generator, it
will generate the required amout i.e 50kw of power to
supply the load. This can be done by the controllers kept
at the generator.
If we connect the load of more than 100kw it will trip out
Is This Answer Correct ? | 41 Yes | 5 No |
Answer / rvg.msceb
Generator is only an energy converter. The generator rating
100KW is specified is max. rating with pf. of 0.8( as per
manufacturs std.)
During the starting no DG set runs with full/partial load.
and it just generate the power required to meet the losses
only. Once after we connects load, it will generate power
required to meet the losses and output. The same equivalent
amount of mechanical power will be consumed from the prime
mover according to the efficiency of the system. So there
is no such question of 50KW energy wastage. Ultimately,
governer of prime mover plays an important role over DG
set.
if we connects more load say 200% of full load, for a
specified time according to the insulation and winding
temperature and prime mover output capacity, the DG can
function, say max. 2-3 minutes. Beyond that, DG will be
shutdown because of higher temp./or out of synchronism.
Is This Answer Correct ? | 31 Yes | 1 No |
Answer / bhavesh and rajendra
If we connect 50 KW load to the 100 KW generator at that
time generator will generator 50 kw by restricting its
turbine fuel input and its efficiency will reduce
If we connect more than 100 Kw the frequency of generator
will go down and its power angle will shift to 90 deg and
its operating torque equal to pull out torque and generator
coms out of sysnchonism and it will trip
Is This Answer Correct ? | 19 Yes | 4 No |
Answer / selvan
It wil genarate only 50kw,if it generates 100kw, we can
load 50kw.if it connected more than 100kw it will tripped
automaticaly.bcause its ferequency go low and also lead the
rated current value.222
Is This Answer Correct ? | 7 Yes | 2 No |
Answer / gaurav naik
It will generate only 50kw i.e power consumed by load
At this condition mechanical power required to rorate
alternator will be half of that at 100KW
So speed may go high (rpm)
This is controlled by centifugal governors in Gensets
Is This Answer Correct ? | 9 Yes | 5 No |
Answer / erharisheee51
First one thing understand clearly.Generator Generates only
voltage say 11kV for ex .. so it will convert to power its
depends on the load. so if the Load increases automatically
generator terminal voltage will go down & Frequency (speed)
.so you have to increase the excitation voltage to maintain
the terminal voltage normal , if the load is less u can
reduce the excitation no need of wasting external power
(excitation voltage) also.
so i guess if the load is low r high..there is no change in
generator generation it will generate the fixed voltage ..
and the Bill will maintained only usage not generation so i
if they used 50 kw they will charge for the same , remaining
50 kw u have saved.thats it..
Please leave a commnent for this :)
Is This Answer Correct ? | 3 Yes | 2 No |
Answer / madhulathaoshapaka
Under steady state conditions, the (mechanical input - rotational losses) will be equal to the electrical power output. Hence, the generator will generate only 50 kW, even though its full capacity is 100kW.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / raviteja nowduru
for such type conditions speed governing system will come
into picture.so generator will generate only 50 k.but all
industries will generate the full load kw and they supply it
grid to which they are connected.
Is This Answer Correct ? | 2 Yes | 3 No |
What will be MF for below rating ? Main CT PT value is 11kva/110 and 20/5 amp Meter display is 1kva/110v and -/5 amp What will be MF ? Multiplycity factor of energy meter
why two point starter,three point starter, four point starter cannot be used for A.C machines?
what are the types of transformers
what is S.T?specify the range?
what is power and what is watts detailed description and formulas
mccb service sittings be done?
how the phase convertor changes the no. of phases
What are the earthing required for commissionthe DG Set?
For a stable system, where should the poles of a system be in a root loci plot?
how to meas-our losses for L.T & H.T
What is the Difference Between choke & ballast
3 Answers ABB, ICS Integrated Computer Solutions,
Why restricted earth fault protection is needed? Why can’t differential Protection is sufficient?