I have suguna 3 hp pump for my agreeculture work.It deliver
the water from 45 feet well .I suffered by powercut.During
powercut i got 2phase supply only .My question is can i
run the pump in 2 phase supply using capacitor?.Can u
explain me how to connect the capacitors?
Answers were Sorted based on User's Feedback
You can also use capacitors to create a "phantom" 3rd phase
from the other 2. This may be what you have seen, but what
you probably didn't know is that this severely robs the
motor of power capacity. The motor runs severely unbalanced
and has a lot of what are called "negative sequence
currents" because of the 1 phase power and because the sine
waves are 180 degrees apart on the 2 "real" phases,
compared to being 120 degrees out on true 3 phase. Negative
sequence current produces negative torque in the motor and
causes heating without doing useful work, meaning that it
will severely overheat under load. For this reason, you
must derate the motor by at least 50%, some even say 66%.
So that means if you have a 15HP motor, you had better not
need more than 7-1/2 or even 5HP out of it if you are going
to do this.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / electrical alie
It is know form physics that you can provide water about 45
ft away. This is clear from the objective test that is run.
However when you try to sole this problem from the books
you have read, you find conflict. This is because if i
tried solve objective from the other book then i could not
solve this from the 3rd book. Therefore you must use the
motor curves that power the overload system to determine if
you unknown will operate properly. It will help if you can
determine what is standard height of an energy meter is
from ground.
| Is This Answer Correct ? | 1 Yes | 1 No |
I have 3KVA Libert GTX2 UPS. I need to calculate the back up time with some load. How to calculate the Back time. I need the expert guide
why transformer does not obey ohm law?
what are the safety of chiller.
What is inrush current? how can calculateit? what is the affect of it?
Will transformer heating be approximately the same for resistive, inductive or capacitive loads of the same VA rating? Explain.
How to calculate of maximum demand if given 628kw, 785kva, 0.8 p.f.
can any one provide me a connection wiring diagram for a DG set control panel along with BOM?
Isi standard of lux level required / to be maitained in different working place general & in textaile industry.
To prevent the mal operation of a differentially connected relay while energizing a transformer, the relay restraining coil is baised with (a)second harmonic current (b)fifth harmonic current (c)third harmonic current (d)seventh harmonic current
3) How earthing is done? How it measured? Write the method for earthing? How the earth resistance is kept low?
How out of step protection relay works?
Why in metering Ct for ammeters ct secondary side is grounded for each Ct but not in case of CBCT (Core balance current transformer)..kindly some1 highlights the reason..is it because net flux is zero?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)