Answer / welcome4ujd
dry contact is that the contacts are floating. One example
is the COM, NC and NO contacts of the relays. If no voltage
is connected to them, it is called dry contacts.
Volt-free and dry contact mean the same thing. If a control
system supplier offers a dry contact for you to read as a
status bit, then he is offering to close a contact (relay
or contact output) that is nothing more that a stand-alone
set of contacts with no voltage, current, or anything else
impressed across the contact set. It becomes the user's
responsibility to determine how to sense that contact
closure. Usually you do this by putting a voltage on one
side and sensing the voltage on a return line from the
other side of the contact when it closes. Once you apply
voltage to the contacts, it becomes a wet contact.
You "wet" the contact with a sensible voltage level.
.
| Is This Answer Correct ? | 86 Yes | 7 No |
Answer / abhijeet
Dry Contact means contact before connecting voltage signals....while as Wet means connecting instrument in Circuit...!!!!!
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / greg gertsch
It has been my understanding; Dry contacts when open do not
transfer any voltage or currant to the load side.
wet contacts have voltage on the load side but no currant
flow. Such as when a varistor is used as a bridge allowing
line voltage to cross over to the load side which minimizes
the arcing on contact points
| Is This Answer Correct ? | 0 Yes | 7 No |
Answer / einstainn
when you dips the contact into liquids then we call them wet
contact..hahaha
| Is This Answer Correct ? | 3 Yes | 23 No |
I heard that we can use flow transmitter for level measurment also hw it is?
meaning of SMART
If I want to buy a pressure switch & 3-way valve for hot water application then witch parameter I should consider.
IF TX SHOWS SLOW RESPONSE, WHILE A CLOSE LOOP AND WHEN WE PUT THE CONTROLLER ON MANUAL THE PROBLEM RECTIFIED, SO WE CAN SAY THE PROBLEM IS IN
What is require for PLC Programming?
what is the process for double acting cylinder pneumatic for 32' v/v
How to convert Differential pressure to flow in TPH
What is the purpose of LO overhead tank in turbines.
What is standard of DCS panel design?and what is step of DCS panel design?wiring and type of connector(screw or DB connector)
Definition of level
Q1: Consider part of a control loop, which excludes the transmitter, consisting of a process, a controller and a control valve which may be represented by two dead times of 0.5 min each and three exponential lags of 0.8 min., 1.0 min. and 1.5 min. respectively. We wish to express this system as an overall first order plus dead time (FOPLD) model ie gain, time constant and process dead time. (We will see later that this is often done, to simplify controller tuning). For this exercise, gain is considered to be 1.0. (A) If the transmitter is a flow transmitter whose behaviour can be described by a dead time of 0.2 min. and an exponential lag of 0.5 min. in terms of the overall dead time and overall first order lag how can the system behaviour be approximated ? Overall dead time = Overall time constant = (B) If the transmitter is a temperature transmitter with a temperature sensor in a protecting well whose behaviour can be described by a dead time of 0.7 min. and an exponential lag of 15 min. how can the overall system behaviour be approximated now? Overall dead time = Overall time constant =
what is meant by nuclear power plant?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)