L&T ACB C-POWER OF 800A FAULS TRIPING AT THE TIME OF 110KW
MOTOR STARTS WITH EARTH FAULT RELEASE
Answer / sudhakar g
HI,
First you have to check the settings of ACB breaker, If the
settings fault also it will be tripping. The following
settings you have to check in ACB are
1) Thermal Protection against " Overload faults ": Ir = 0.9
X 800A= 720A-Time delay = 2 sec
2) Magnetic Protection for " Short Circuit Faults " : Isd =
3 x 800A = 2400A- Time delay = 2 milli sec
3) Earth Fault Protection against direct fault between any
phase and the protection line : Ig = 200A (D)-Time delay = 2
milli sec
4) Instantaneous Protection against " Short Circuit Faults "
li = 3 x 3200 = 9600A for Big faults
I am taking Electrical desining classes in Bangalore...It
will be usefull for designing as well as site engineers
those who are intrested to go for Electrical
Engineers....we give you indepth knowledge of Load calu,
Cable sizing, Lighting cal, panels, breaker
selection,Autocad drawing....if any body intrested means
pls call to +91-7760362623 or sudhakar28485@gmail.com
Is This Answer Correct ? | 0 Yes | 0 No |
The control system is used for?
What is AVR in Turbo generator in Thermal power plant?
fuses rated by amperes but not power,why?
what happend to DC shunt motor if its field winding insulation becomes slightly weak? will that motor can run on full load or not explain in detail. thanks
what is v/f control in VFD?
what is invertor supply and raw powersupply
Wy transformer ratings are in multiple of 11 always?
What device is use for metering current at lt consumer end..??
1hp single phase load = howmuch 3 phase load
what is meant by substation?
Is the theorem applicable to ac sources?
What mean by MLTP