L&T ACB C-POWER OF 800A FAULS TRIPING AT THE TIME OF 110KW
MOTOR STARTS WITH EARTH FAULT RELEASE
Answer / sudhakar g
HI,
First you have to check the settings of ACB breaker, If the
settings fault also it will be tripping. The following
settings you have to check in ACB are
1) Thermal Protection against " Overload faults ": Ir = 0.9
X 800A= 720A-Time delay = 2 sec
2) Magnetic Protection for " Short Circuit Faults " : Isd =
3 x 800A = 2400A- Time delay = 2 milli sec
3) Earth Fault Protection against direct fault between any
phase and the protection line : Ig = 200A (D)-Time delay = 2
milli sec
4) Instantaneous Protection against " Short Circuit Faults "
li = 3 x 3200 = 9600A for Big faults
I am taking Electrical desining classes in Bangalore...It
will be usefull for designing as well as site engineers
those who are intrested to go for Electrical
Engineers....we give you indepth knowledge of Load calu,
Cable sizing, Lighting cal, panels, breaker
selection,Autocad drawing....if any body intrested means
pls call to +91-7760362623 or sudhakar28485@gmail.com
| Is This Answer Correct ? | 0 Yes | 0 No |
can we charge 3 ph power transformer delta-star wound with neutral grounded 6.6kV/415V from secondary side(415V) but with primary(6.6kV) open by dg,what are the disadvantages or losses.
When we use PT in HT Panel why the ratio is 11Kv/√3/110v/√3 please explain briefly with suitable formula?
We have two 1 phase heating coils having same resistance of 25ohm, but during operation one takes 3A and other 6A Is it posiible Pls. explain
If Ac supply is given to the DC motor then what will happen? clear explanation
Why we have short circuit the secondary of the transformer
IAM GOING TO ERECT THE STREET LIGHT.,, I NEED HOW TO CALCULATE LUX., ILLUMINATION.,AND ALL
Transformer how to maintaince a check b check c check d check
Is there a standard depth of gravel fill in Substation Switchyard? Please give a design/drawing. Thank you.
Is vtg is controlled by the resistor? if else how much?
grr resistance & contrator malt continuous
why transformer not used to starter
Is any generator is developed which is operated with out diesal or other expensive source?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)