How much duration I can keep open the CT if it is under
loading condition(100 Amp load)?
Answers were Sorted based on User's Feedback
Answer / vijay
If CT IS OPEN UNDER LOADING CONDITION IT WILL BURST.
Is This Answer Correct ? | 6 Yes | 0 No |
when ct is open circuited there is more voltage at the open
ends. this voltage may dangerous, if touch it you feel
sevior shock. The ct turns will act secondary itself & the
voltage will be equal to
voltage at bus or cable X No.of turns of the ct
which leads to leathal voltage & the current path is open
thus circuit is not completed.We aRE using ct's for metering
& protection. The metering ct will not get saturarated after
its rated VA immidiately but the protective ct's are GET
saturarated after its rated VA.
Is This Answer Correct ? | 2 Yes | 0 No |
Hy the hydro power stations have high transmission and Distribution costs?
FOR 16/20 MVA 132/33 KV ONAN/ONAF TYPE TRANSFORMER IT IS DESIGNED FOR 16 MVA WITH ONAN CONDITION.IT BECOMES 20 MVA UNDER ONAF CONDITION.LOAD LOSS IS GUARANTEED FOR 65KW AT 20 MVA AND % IMPEDANCE 13.75. PLEASE TELL US AT WHAT LOAD LOSS AND % IMPEDANCE IT SHOULD BE DESIGNED FOR 16 MVA AND WHAT WILL BE ITS EFFICIENCY AT 20 MVA?
what is distribution board?
In Fluorescent tube there is a writing like 6500k . what this 6500k represents?
What is the selection & Designing procedure for DG/Transformer
4 Answers Crompton Greaves, Sterling, TATA,
how fluoresent lamp works??
list the type of vfd? wich is sutable for heating kiln?
why the transformer connected like STAR- STAR, DELTA- DELTA, STAR- DELTA, DELTA-STAR ...? why these connections ,,, explain the advantages these connections?
why we remove capacitor connection in 3 ph Induction Motor while taking noload test.
what's the difference between induction generator and synchronous generator?
how to extend relay operating timing in 24V dc relay card (without using Timer )
What is genrally the % Impedance of a Dg set? How can we calculate Earthing conductor size for a DG set?