why cant we use mV instead of mA?
Answers were Sorted based on User's Feedback
Answer / kishore kumar
Distance is the main concideration, as distance increases
voltage drop will be increased where current remains same
Is This Answer Correct ? | 76 Yes | 1 No |
Answer / rakesh kumar n
There won't be any current drop in mA, but when you consider
Voltage there will be Voltage drop.
-->main Reasons for Voltage drop
#Distance between the Field and Control Room(more the
Distance and more will be the Voltage drop)
#Consider if the Distance is small between the Field and
Control room,then also there will be Voltage drop,because it
is milli Volt
#Theory Sum of the incoming current and Out going current
is always Zero 20mA=20mA by KCL, if you find any thing
wrong,you can check it in Transmitter Outlet and the DCS
Inlet will have the same milli Amp.
Thank you
Rakesh Kumar.N
INSTRUMENTATION ENGINEER
Is This Answer Correct ? | 10 Yes | 1 No |
Answer / mahesh soni
Distance is the main concideration, as distance increases
voltage drop will be increased where current remains same
due to ohms law there is
I=V/R SO CURRENT VWILL SAME any time or no lossed by
wire resistance so v can lay cables long root laying in
plant& all instruments draw curren not voltage
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / mohammed abbas
As length of the cable increses the line resistence also
increse, but the current remain same, suppose if your
using the long cable assume 50mtr the line resistance
assume 2 ohm for 50mtr, for 100mtr the line resistance will
be double 100=4 ohm. as per ohmns law. if you are measuring
the flow parameter for 50 mtr and another 100 mtr for same
process condition the reading will be diffrent, suppose if
your are using millivolt means but milli amps will remain
same.
the volatge will increse or decerse as the lenghth incerese
of decerses, but current remain same that is what milli
amps will be used
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / pankaj kumar (iert)
* voltage pickup more noise as compare to current.
* if we use voltage signal then chance of its drop.
*
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / mohammed
because we cannot lay a cable for more than 50 m to carry mV
signal whereas we can connect current signal cable because it
is less diameter, will not affect by noise and not costly in
addition can be connected for long distances
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / delta_v
That's due to voltage drop :)
As simple as that...
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / shankar prasad p
MV if transmitted over long distance in wires, voltage
drops occurs leading to variation in actual value.where as
if we transmit mA signal over cable voltage drop not takes
place so we can get actual readings.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ashutosh
in series the current remain same so the loss of current
due to wire res is not into the consideration in mA but it
is there in mV
Is This Answer Correct ? | 2 Yes | 3 No |
what is difference between OP AMP and differential amplifier?
why are use only 4 to 20ma. signal.
if the t/c o/p is 4-20mv then how plc recognize it because we are dealing with the 4-20ma in the plc ????????????????
How will you select suitable Instrument for Process line/Tank/Vessel?
Valve positioner and actuators in detail.
HOw To Use 24V DC in Instrument?
in which principle pressure tx,level tx ,flow tx,temp tx ,control valve works?
How do bending tubing provide better measurement than using tubing fittings such as elbows?
how does pressure is converted into milli amps in pressure transmitter? plzzz explain practically
i install a DP transmitter of Faugi on drum level of boiler but i face a problem in it when i engergize the transmitter the meter shows 0 or 100% no variation in it.the distance of two points is 19.5 inches, i am in trouble please suggest me what can i do it's very urgent Please reply me as soon as possible Best regards ikraam haider
how commission a transmitter evev plant is already running
what are the levels of automation?