In field side transmitter voltage droping here no loose connection then what will happen?
Answers were Sorted based on User's Feedback
The minimum required loop voltage depends on the voltage needed to drive 20ma (or 21.5mA if fail-safe high is used) through the total loop resistance.
Even if the power supply voltage sags/drops slightly, it is still possible that the loop will function properly, because it depends on the actual loop resistances and the lift-off voltage required by the transmitter
If there is not sufficient loop voltage, it will become apparent when the transmitter fails to go above a certain milliamp output, because there is insufficient voltage to drive more current through the loop's total resistance.
In some cases of low loop voltage, a field transmitter will cycle on and off, re-initializing each time it fails to push sufficient current because it is voltage-starved.
If the loop wiring is sized properly, then a voltage drop is likely due to
- a bad connection in junction box
- in some cases a ground loop from damaged wire insulation
- adding too many additional loads - more transmitters than the power supply is rated for
- failing power supply
- adding another device in series in the loop, like an indicator, recorder, or I/O module input that pushes the total loop resistance too high. Carl Ellis
Measure First
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / vinay
distance betwn. control rm. and transmitter may be larger or much as much recmmnd.
Sol:-
Use the amplifier or isolator in btwn them (rm. to tx.)
| Is This Answer Correct ? | 4 Yes | 1 No |
HOW TO CONVERT 0-60KG/CM2 PRESSURE TRANSMITTER TO A LEVEL TRANSMITTER? CAN WE ABLE TO DO IT? IF YES HOW TO DO IT BY USING HART?
What is Cryogenic?
I have a close vessel tank which is under vaccum when in running condition so pl. Provide it's range for dp type tx whose flange to flange distance is 440 mm and density is 1
which type of filter gives the constant phase characteristics?
why direct mounted pressure transmitters is always installed with DBB ( double bleed block) valve in process line or top of the tanks ?
What is the difference between compensation and extension cable.
Explain about safety integrated level protection? . How it was differ from other protections ?
why we use 0.2 to 1.0 kg/cm2 output in control valve
how to check thermocouple ,its working or not?
14 Answers Coca Cola, Ford, Honeywell,
How to set up the various advanced process controllers, input the proper parameters, and tune those controllers given related control system information.
How to gennerate earth leakage monitoring alarm for solenoid valves in control system?
What is surge in compressors? How to detect and control it?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)