What shall be minimum thickness of firewall in between two
transformers and which code specifies it ?
Firewalls between transformer (Firewall) shall be provided with 230mm thick RCC or 355mm thick brick wall.
You can refer NFPA 850 for reference.
Is This Answer Correct ? | 9 Yes | 1 No |
What core magnetic balance test of transformer? How to do this test in a three phase Star star (star-LV, star-HV) transformer? How to measure and where to measure?
WHAT IS SITTING AMPS IN OVER-LOAD RELAY FOR 1PH OR 3PH MOTORS?IF ITS NAME PLATE GIVEN MAX AMPS 10AMPS?
why the earth is taken minimum in supplying? wather it the proportional factor to getting work any equipment or a power plant?
why we avoid parallel operation of diesl generator?
What is the criteria for deciding whther fire wall is required between two power transformers