Are same transformer be employed for step up and step down
services?
Answers were Sorted based on User's Feedback
Answer / bajrang ahirwar
NO
same transformer can't be used for both operations.
exception is ICT like 220KV/400KV
ICT is inter connecting or interposing transformer, these type of transformers are specially designed.
there no load an on load losses ane calculated so that they can be operated from either side.
on the other hand if have a 2000 KVA 11kv/440V 0.85 pf step down transformer:
current in hv side will be = 123 A
and current in LV side will be =3087 A
the secondary has to bear heavy current so it is designed accordingly with Thick winding.
and HV Primary has to carry a comperatively low current so its windings are of thin windings.
NOW the reverse operation
the heavy winding will be connected to high Voltage 11 Kv side, fine no problem, because it has to carry a lower current of 123 A ans secondary is rated for 3500 A approx.
BUT
the thin wired high voltage winding will now have to supplly the larger gurrent 3080 A, this winding has also larger losses R=Rho L/A
result??
the winding will burn out.
so practically it is not possible.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / iamdon
Strictly speaking No.
Most transformers rated above 3kVA can be used either as
step up or as step down depending upon the need.
But transformers rated below 2kVA can be used only for one
operation for which it is designed.It can not be employed
in revese(with respect to design) transformation,because
the winding used is compensated which will not work
satisfactorily in reverse.
Author:arbelectbit@yahoo.com
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / kushal
if we are using the same rating of transformer for same line
then only we can use it in both the ways otherwise if u say
that the distribution transformer can b used as a power
transformer just by changing its primary to secondry or vice
versa its not possible.
a transformer is the only device which can b used in step up
and step down both the ways.
| Is This Answer Correct ? | 0 Yes | 2 No |
whats is MARX CIRCUIT?
why u want to work in sail/ntpc as u r already in an it company where life is good, good environment no much tensions etc?
WHAT IS THE FUNCTION OF PULSE TRANSFORMER IN DC DRIVE
how to size a diesel generator set?
Can someone tell me how to calculate the size of a power cable? What are the factors involved in cable sizing?
when running 2 nos 450kva dg sets in parallel operation ,in one Dg set power factor and Kvar going to lagging and ampere suddenly going high,please give me suggestion to correct the same.
What is the difference between MCCB, ACB & VCB
sir, Is their any measuring unit of knoking? please explian?
what is the difference between 3 phase 3wire &3phase 4 wire meter?what is the advantage of 3p3w over 3p4w?
What are the Steps for Testing of 20MVA (make:-CGL) Transformer? How many Test we have to do?
How to calculate motor current for 3 ph & 1 Ph motor from KW rating?
while buying 30 kva on line ups for 1 phase ouput, we ave to calculate the number of batteries for 2 hours back up? how to calculate the ah rating and number of batteries
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)