In sub-station how to find multifactor of panel?
Answer / s kannan
MF is not for panels for relays and meters only. Meters will be connected with CT and PT's secondary. If we want to calculate MF for meters like Voltmeter and Ammeter Just follow the formula Mf= CT Ratio X PT Ratio.
Eg:
CT Ratio: 600-300/1-1A(Adopted ratio is 300A as primary) PT Ratio: 33KV/rt3/110V/rt3/110V/rt3
Then MF:(300/1)X(33000/rt3/110/rt3)
(300/1)X(33000/1.732X1.732/110)
(300)X(33000/110)
(300)X(300)
90000
Means Multiply the particular meter's reading by this 90000 for obtaining the genuine value.
Is This Answer Correct ? | 0 Yes | 0 No |
Hello Can I use step up HV transformer 440/4160V as a step down? Thanks Evgeny
what is phase shifting transformer.
if we want to increase the back up time of an UPS what should we do ? if we want to decrease the charging time of a battery/batteries attached with the UPS what should we do ?
Why transformer use to generator neutral earthing purpose ?
When we synchronize the Generator BKR with TIE BKR then Gen BKR is hold but TIE BKR is Tripped on Non directional over current but when TIE BKR is Syn. with Gen. BKR then no fault occur so what is the problem
which protection function should measure RMS value of current&DFT value of current?
How to put breaker in service / test position.
i have completed deee and i've (June2012-feb 2015 experience in electrical maintenance in pvt ltd company.company having HT & LT electrical power.how to apply electrical C-license ,NOW I was resigned my job,what are requirements of applying for c-license
HOW TO CALCULATE THE CAPACITOR RANGE FOR LOAD FOR PF IMPROVEMENT? EXPLE:FOR 65 HP LOAD HOW TO CALCULATE CAPACITOR RANGE?
12 Answers Al-Malik, All Star Electric, GEC, Reliance, Universal Industries,
what is the difference between megger and earth tester?
28 Answers Ashok Leyland, IOCL, RRL,
sigal phase supply is 230 v ac two phase supply is 415 v ac then why three phase supply having supply is 415 v ac why not 690v ac
what is different between installation and commonissonig.