State the difference between Surge Arrester and Lightning
arrester,Both are same or not?
Answers were Sorted based on User's Feedback
Answer / s bhattacharya
LIGHTNING ARRESTOR IS NOT SUPPOSED TO CONDUCT AT POWER
FREQUENCY.
WHEREAS SURGE ARRESTORS ARE SUPPOSED TO CONDUCT AT POWER
FREQUENCY.
THIS IS THE FUNDAMENTAL DIFFERENCE .
| Is This Answer Correct ? | 42 Yes | 6 No |
Answer / faisal
Surge Arresters are widely also known Lightning arresters.
However strictly speaking the two are in fact different. Surge arresters are devices installed on Over head lines, substations etc to avoid a surge of an additional current/ voltage/charge due to various faults occurring and since one of the major reasons of a surge is due to lightning these surge arresters are also coined as Lightning arrester.
However Lightning arresters are separate instruments specifically designed for protection of structures solely from lightning this equipment neutralizes the charge by nullifying the charge it receives from the lightning and grounds it.Lightning arresters don't intervene with the excess current / voltage surge due to electrical faults - it is solely for LIGHTNING protection unlike surge arrestors which is a protection against electrical faults and Lightning which is a natural charge dispenser
| Is This Answer Correct ? | 27 Yes | 6 No |
Answer / hms
The main differences between a lightning arrester and a surge arrester are time and position. In the past, there were only lightning arresters, since lightning was the only place where big power surges would come from. Now, a lighting arrester typically prevents surges from outside the electrical grid, and a surge arrester prevents ones from inside.
"Both are doing the same job,but both are not same".
A surge arrester is device that intercepts electrical surges and sends the spike to ground before it can hurt a connected device. These arresters are also known as surge protectors or lightning arresters, but there are some very small differences between these devices. In most cases, when a surge arrester intercepts a power surge, it fuses itself to prevent transmission. This will stop the surge, but it also destroys the surge arrester. If the arrester is improperly installed, this fusion can cause more problems than the initial surge.
| Is This Answer Correct ? | 9 Yes | 3 No |
Answer / anil yadav ptrjtpc.
Surge absorbor is max time lighting and light sresstor is limiting time is lighting..
| Is This Answer Correct ? | 0 Yes | 4 No |
Answer / priyanka dhar
Lightning arresters are installed inside the distribution
board and they protect against surge volatges in case of
direct lightning strikes.
surge arresters are installed in sub-distribution board as
well as in terminal equipment thus protecting against surge
voltages due to distant lightning and due to internal
switching operations respectively.
| Is This Answer Correct ? | 3 Yes | 13 No |
Answer / gunasekaran
if we using outdoor substation that is LAS if we use indoor
or switch gear that is surge arr ester both are not
conducting power frequency over voltage
| Is This Answer Correct ? | 1 Yes | 14 No |
Why the vector group of excitation transformer in static excitation system is Dy5?
I have 3 1000 kva single phase transformers and I wish to replace them with one three phase transformer. What is he kva rating of the new three phase, is it 1000 kva also or 3000 kva.
What is the maxvoltage drop allowed at any healthy joint at full load ?
When induction motor is started,we see all other electrial appliances connected on the same supply are dimmed out for some moment why?
If OLTC is in manual position there is chance to variation of voltage(Low or High)?
How to run 1ph motor(230 VOLTS its full load amps is 4.5 ampa))with 480 volts main(we didn hav neutral)Thn we go for step down transformer.Our load 10 amps,so we conisder this amps in primary are secondary side?
Neutral CT for 45MVA 132/11 KV YNd11 Transformer. NCT REF CLASS-PS or 5P20 with 20VA burden which is suitable.
What is the % number of various buses in a typical power system?
True or false question. 1.The fuse provide phase and neutral 2.power loss in electrical circuit can take place in (resistance or inductance or capacitance). 3.two phase system each phase has separated by a phase difference of (90 or 180 or 270 or 45). 4.3 phase balanced star connected load neutral current shall be (line current or phase current or zero or unity)
how could we calculate the no of outgoings from a 800 watt distribution board
why genarator genarating voltage 11 KV?
What do you mean by isolators and circuit breakers?
6 Answers Bhushan Power Steel,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)