Can any one help me how to set an overload set the range from 2.8A to
4A , rated motor current 22A, CT 60/5A
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
ct ratio is 12, hence full load current is measured as appx
2 amps by ct.You have to replace ct with 40/5 A or 30/5 A
ratio.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / thirumoorthy s
the CT ratio is for metering only. so we cant set the O/L
setting for ur (2.8-4)A relay. u should provide correct O/L
relay. ie (18-25)A. the rated rating 22A, So we can set it
ion 20A.
| Is This Answer Correct ? | 3 Yes | 4 No |
What is the Diff. btw Manule Pull Station & Manule Abort Station Switches used in FM200 System??
How to synchronization will be done between two DGs ?
What is tan delta point of transformer?
sir can you operated Transformer on frequency from that for which is design?
What happens if i apply 500V to 440V rotary Switch ?
how many voltage or current enough to kill a person?
domine+aptitude test means?
What is mean by vector group? For what purposes we doing vector group test in transformers?
what is the working principle of UPS?
why ups rated in kva
what is use of lockout relay in ht voltage
what kind of quetions will ask in BHEL in interview? Plz help me?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)