Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


HOW TO CALCULATE THE CAPACITOR RANGE FOR LOAD FOR PF
IMPROVEMENT?
EXPLE:FOR 65 HP LOAD HOW TO CALCULATE CAPACITOR RANGE?

Answers were Sorted based on User's Feedback



HOW TO CALCULATE THE CAPACITOR RANGE FOR LOAD FOR PF IMPROVEMENT? EXPLE:FOR 65 HP LOAD HOW TO CAL..

Answer / deepakindi1

Boss what if u dont have the table?

let Cos(@1) be the present PF

@1=cos'(@1) (cos inverse)
let Cos(@2) be the desired PF
@2=cos'(@2) (cos inverse)


KVAR required= KW[ tan(@1)-tan(@2)]

for 65 Hp load
KW= 65HP*0.746 = 48.49KW
Considering Preent P.F=0.50
desired pf =0.99
ie cos(@1)=0.5
@1=cos'(0.5)=60
@2=cos'(.99)=8.1

kvar=48.49*[tan(60)-tan(8.1)]
=48.49*[1.732-.142]
=77.08

kvar=77.08

Is This Answer Correct ?    54 Yes 6 No

HOW TO CALCULATE THE CAPACITOR RANGE FOR LOAD FOR PF IMPROVEMENT? EXPLE:FOR 65 HP LOAD HOW TO CAL..

Answer / mahesh sonawane.

Capacitor range is actually given in Kvar, so to find that
range in kvar

As we know
Power factor = KW/KVA
for 65 Hp load
KW= 65HP*0.746 = 48.49KW
Considering Preent P.F=0.50
Target pf =0.99
Multiplying Factor by standard table= 1.59
Kvar= 48.49 KW * 1.59 = 77.09 Kvar

hence for the load of 65hp, capacitor range will be 77.09
Kvar.

Is This Answer Correct ?    73 Yes 27 No

HOW TO CALCULATE THE CAPACITOR RANGE FOR LOAD FOR PF IMPROVEMENT? EXPLE:FOR 65 HP LOAD HOW TO CAL..

Answer / bala123

please mention the existing powerfactor....

Is This Answer Correct ?    30 Yes 9 No

HOW TO CALCULATE THE CAPACITOR RANGE FOR LOAD FOR PF IMPROVEMENT? EXPLE:FOR 65 HP LOAD HOW TO CAL..

Answer / girish kumar samal, hindalco,h

as pf not giving ,taking pf 0.8
let pf of load =0.8
kw of load= 65 hp=65*0.746=48.5kw
kva =48.5/0.8=60.625kva
kvar =sqrt(60.625^2-48.5^2)=36.375kvar
if we want to improve pf to 0.95 then
improved kva= 48.5/0.95=51.052
improved kvar= sqrt(51.052^2-48.5^2)=15.9411
requard capacitor range = 36.375-15.94=20.43kvar.

Is This Answer Correct ?    26 Yes 12 No

HOW TO CALCULATE THE CAPACITOR RANGE FOR LOAD FOR PF IMPROVEMENT? EXPLE:FOR 65 HP LOAD HOW TO CAL..

Answer / chandru

In This case no other detail is given except the power
rating .

Therefore pf=( KW/KVA)
In order to get incentive and good power factor it is
required to maintain power factor above 0.95

So we take pf=0.95 and kw=(65*0.746)=48.49
Therefore KVA= 48.49/0.95 = 51.04

We know that KVAr= Squareroot( (KVA)^2-(KW)^2)


Therefore KVAr = sqrt(51.04^2-48.49^2)

=15.90 approx..


Capacitor required = 16KVAr.

Is This Answer Correct ?    11 Yes 11 No

HOW TO CALCULATE THE CAPACITOR RANGE FOR LOAD FOR PF IMPROVEMENT? EXPLE:FOR 65 HP LOAD HOW TO CAL..

Answer / manish deswal

let us conside current p.f = .8 & improved to .9,
Load = 65 hp =65 * 746 = 48.49 KW
KVA1 = 48.49/.8= 60.61

KVAR = Squareroot of [ square(60.61)-square(48.49)]=36.36
KVA2 = 48.49/.9= 53.88

KVAR = Squareroot of [ square(53.88)-square(48.49)]=23.49

Increased Capacitor bank capacity = 36.36-23.49 = 12.87 KVAR

Is This Answer Correct ?    3 Yes 3 No

HOW TO CALCULATE THE CAPACITOR RANGE FOR LOAD FOR PF IMPROVEMENT? EXPLE:FOR 65 HP LOAD HOW TO CAL..

Answer / sonu

Deepankandil why we are subtracting initial-final. littele
bit confusion. please throw some light on this issue.
because it will depand on lagging or leading?

Is This Answer Correct ?    3 Yes 6 No

HOW TO CALCULATE THE CAPACITOR RANGE FOR LOAD FOR PF IMPROVEMENT? EXPLE:FOR 65 HP LOAD HOW TO CAL..

Answer / ram lal

power factor is not mention so how can calculate ...........

Is This Answer Correct ?    4 Yes 7 No

HOW TO CALCULATE THE CAPACITOR RANGE FOR LOAD FOR PF IMPROVEMENT? EXPLE:FOR 65 HP LOAD HOW TO CAL..

Answer / naveen kumar mishra

first we should calculate the load(inductive or capacitive
or resistive).
in case of resistive load-----
in case of resistive load the, actual power factor will be
01(maximum),in this case the voltage will linior with
respecte to load current.
so tatal resistive load is(in example 65 hp),
so total load in kw = 65*0.746
=48.49.
As we know
Power factor = KW/KVA
for 65 Hp load(if pure resistive)

Considering Preent P.F=1
Target pf =0.99
Multiplying Factor by standard table= 1.56
Kvar= 48.49 KW * 1.56= 75.64

hence for the load of 65hp, capacitor range will be 75.64
Kvar.(in pure resistor).

Is This Answer Correct ?    2 Yes 5 No

HOW TO CALCULATE THE CAPACITOR RANGE FOR LOAD FOR PF IMPROVEMENT? EXPLE:FOR 65 HP LOAD HOW TO CAL..

Answer / sudhakara

MR. girish
What is meaning of sprt and that calculation

Is This Answer Correct ?    5 Yes 9 No

Post New Answer

More Electrical Engineering Interview Questions

i purchase a microwave which is 50/60Hz but Current Setting 60Hz in my country we usually use 50hz, can i use AVR to solve my problem?

2 Answers   Samsung,


Define delay time.

0 Answers  


Sir we are using 250 kva DG its Diesel consumption 25 lits / hrs maximum load 160 kva now how to calculate units/ litres

1 Answers  


What is Earth Fault and Over current Fault.

1 Answers  


how does directional relay work incase of ac ?

0 Answers  


what is Real power and Reactive power ? what is difference between them ?

5 Answers  


george phenomenon of synchronous machine

0 Answers   JU,


What is Diff. btw Cat-5 & Cat-6 Network Cables???

3 Answers   Emerson,


Can you tell me more about pu systems (per unit systems )calculation in large power systems? how to get the base for voltage and power in generator, transformator and transmission lines?

0 Answers  


Can you explain the phase displacement between primary and secondary of power transformer of any vector group(for ex)?

1 Answers  


What are the uses of MCB & ELCB ?

2 Answers  


What are the advantages and disadvantages of short-pitched winding?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)