Answer / deepakindi1
Boss what if u dont have the table?
let Cos(@1) be the present PF
@1=cos'(@1) (cos inverse)
let Cos(@2) be the desired PF
@2=cos'(@2) (cos inverse)
KVAR required= KW[ tan(@1)-tan(@2)]
for 65 Hp load
KW= 65HP*0.746 = 48.49KW
Considering Preent P.F=0.50
desired pf =0.99
ie cos(@1)=0.5
@1=cos'(0.5)=60
@2=cos'(.99)=8.1
kvar=48.49*[tan(60)-tan(8.1)]
=48.49*[1.732-.142]
=77.08
kvar=77.08
Is This Answer Correct ? | 54 Yes | 6 No |
Answer / mahesh sonawane.
Capacitor range is actually given in Kvar, so to find that
range in kvar
As we know
Power factor = KW/KVA
for 65 Hp load
KW= 65HP*0.746 = 48.49KW
Considering Preent P.F=0.50
Target pf =0.99
Multiplying Factor by standard table= 1.59
Kvar= 48.49 KW * 1.59 = 77.09 Kvar
hence for the load of 65hp, capacitor range will be 77.09
Kvar.
Is This Answer Correct ? | 73 Yes | 27 No |
Answer / girish kumar samal, hindalco,h
as pf not giving ,taking pf 0.8
let pf of load =0.8
kw of load= 65 hp=65*0.746=48.5kw
kva =48.5/0.8=60.625kva
kvar =sqrt(60.625^2-48.5^2)=36.375kvar
if we want to improve pf to 0.95 then
improved kva= 48.5/0.95=51.052
improved kvar= sqrt(51.052^2-48.5^2)=15.9411
requard capacitor range = 36.375-15.94=20.43kvar.
Is This Answer Correct ? | 26 Yes | 12 No |
In This case no other detail is given except the power
rating .
Therefore pf=( KW/KVA)
In order to get incentive and good power factor it is
required to maintain power factor above 0.95
So we take pf=0.95 and kw=(65*0.746)=48.49
Therefore KVA= 48.49/0.95 = 51.04
We know that KVAr= Squareroot( (KVA)^2-(KW)^2)
Therefore KVAr = sqrt(51.04^2-48.49^2)
=15.90 approx..
Capacitor required = 16KVAr.
Is This Answer Correct ? | 11 Yes | 11 No |
Answer / manish deswal
let us conside current p.f = .8 & improved to .9,
Load = 65 hp =65 * 746 = 48.49 KW
KVA1 = 48.49/.8= 60.61
KVAR = Squareroot of [ square(60.61)-square(48.49)]=36.36
KVA2 = 48.49/.9= 53.88
KVAR = Squareroot of [ square(53.88)-square(48.49)]=23.49
Increased Capacitor bank capacity = 36.36-23.49 = 12.87 KVAR
Is This Answer Correct ? | 3 Yes | 3 No |
Answer / sonu
Deepankandil why we are subtracting initial-final. littele
bit confusion. please throw some light on this issue.
because it will depand on lagging or leading?
Is This Answer Correct ? | 3 Yes | 6 No |
Answer / ram lal
power factor is not mention so how can calculate ...........
Is This Answer Correct ? | 4 Yes | 7 No |
Answer / naveen kumar mishra
first we should calculate the load(inductive or capacitive
or resistive).
in case of resistive load-----
in case of resistive load the, actual power factor will be
01(maximum),in this case the voltage will linior with
respecte to load current.
so tatal resistive load is(in example 65 hp),
so total load in kw = 65*0.746
=48.49.
As we know
Power factor = KW/KVA
for 65 Hp load(if pure resistive)
Considering Preent P.F=1
Target pf =0.99
Multiplying Factor by standard table= 1.56
Kvar= 48.49 KW * 1.56= 75.64
hence for the load of 65hp, capacitor range will be 75.64
Kvar.(in pure resistor).
Is This Answer Correct ? | 2 Yes | 5 No |
Answer / sudhakara
MR. girish
What is meaning of sprt and that calculation
Is This Answer Correct ? | 5 Yes | 9 No |
why we not used 11kva as a direct our electrnics component.
sir what is the minimum IR value of 11 KV alternator?
why we use the fuse in only one wire? althrough in ac current the current flows in both directions. why the neutral wire can be taken half the magnitude of phase wire while same current returns from neutral wire?
calculation of lad carryinc capacity of 6mm2 cross section wire in 415 voltage circuit. What will be the amps.
why using earth testing rod 15 meter 30 meter long to each other?
which type motor r use in the celling fan.....
what is the disadvantage of leading power factor...why can't we use it (pf=0) for a long period of time?
what is the all safty name of diesel genrator?
How many types of fault occur in a 3-phase power system?
what is NANO TECHNOLOGY?
why DOL starter is use in induction motor as it is not reduce the starting torque
What work have you done on full chip Clock and Power distribution? What process technology and budgets were used?
0 Answers Divis Laboratories, Intel, Sainor Labs,