In rosemount transmitter, open the back side cover which
contains termination.
To check input Power:
switch on the multimeter and select the DC voltage
measurement and connect the positive(red) lead to positive(+
indication in the transmitter) and negative (Black) lead in
the negative terminal(-). then the reading shows 24V DC.
To Check 4-20ma output:
Switch on the multimeter and change the red lead to MA
section and remove one wire from the transmitter and connect
as series. it will show how much reading.
| Is This Answer Correct ? | 6 Yes | 2 No |
Answer / carl_ellis
1) Answer #1 is wrong about testing the power supply voltage
With a 24Vdc power supply, the voltage across the
transmitter terminals will never be 24Vdc because a 2 wire,
loop powered transmitter is a current regulator.
A current regulator operates by changing the voltage in the
circuit to regulate the current. The transmitter consumes
some current to operate (3.5mA) and regulate the loop current.
To repeat, to regulate the current, the voltage MUST change.
A minimum loop current of 4mA MUST drop voltage across the
transmitter terminals, it's basic physics.
If one reads 24Vdc across the transmitter terminals, then
there is no loop current flowing because the loop has an
open circuit!
Typically, the 24Vdc power supply positive connects to the
(+) terminal on the transmitter.
If the transmitter is operating and is wired to a typical
analog input with a 250 ohm input resistance, then the
voltage across the (+) and (-) transmitter terminals will be
23Vdc at 4mA loop current (1 volt dropped across the input
at 4mA)
19V at 20mA loop current (5 volts dropped across the input
at 20mA).
The sum of the voltage drops through the loop must equal the
power supply voltage. 23V + 1V = 24V; 19V + 5V = 24V
If the loop is opened by removing the wire from negative
terminal so that no current flows in the loop, then a
voltage test measuring from positive terminal to the loose
hanging wire (that eventually connects to the negative side
of the power supply) will show 24Vdc because the high
impedance of the voltmeter limits any current to the
pico/micro amp level, practically an open circuit.
So, making a voltage measurement across the transmitters (+)
and (-) terminals will NOT show 24Vdc (the power supply
voltage).
2) To check the milliamp output, it is correct that one can
remove the wire.
But nearly all 1151 and 3051 Rosemount pressure transmitters
have a 'test' terminals whose purpose is to allow a loop
current check without opening the loop.
When a milliameter (+) probe is connected to the (+) test
terminal and the (-) probe is connected to the (-) common
terminal, the milliammeter will indicate the loop current.
Using the test terminals does not break or open the loop
circuit.
A HART communicator will show the loop current, also.
Carl Ellis
Measure First
| Is This Answer Correct ? | 1 Yes | 0 No |
.==PL..PL.. FORWARD TO MANAGER PURCHASE./ / Q.ASSU. DEPT.. =FROM==AJAY ENTERPRISES ===============PUNECITY..INDIA. DEAR SIRS,............. ======================================================== =NEW SUPPLY/ REPAIRING AND CALIBRATION =OF=MECHANICAL /DIGITAL / ELECTRONIC=PRECISION MEASURING INSTRUMENTS=FROM == 22YEARS. ============================================================ = 1.==NAME OF THE COMPANY= AJAY ENTERPRISES 2.=ADDRESS OF THE COMPANY= OFFICE NO 08, DALAL CHAMBERS, MKTYARD PUNE= 411037. ===== TEL- 020 242601! 09. MOB- 0 98900 98941. 3.=EMAIL= ajaygujar1@gmail.com.-- AND-- ajayenterprises1@yahoo.com--- =========================================================== 4.=ACTIVITY OF THE COMPANY= SUPPLIER OF PRECISION MEASURING INST RUMENTS AND MAGNETIC TOOLS IN PUNE== [ MITUTOYO / TESA / KUMAUN / MAHR / BRITOOL / TOHNICHY / DIATEST-GERMANY / IMADA / TECKLOK / SYLVAC /ADITYA=ACCURATE / BAKER/ CRYSTAL / FLUKE-RAYTEK ETC. 5.=SUPPLY= VERNIER CALIPERS / MICROMETERS / HEIGHTGAUGES / SLIPGAGE / BORE DIAL GAUGES / MEASURING PINS / TORQUE WRENCHES / GAUGES.. PLUGGAUGES / RINGGAUGES / SHORE A / D HARDNESS TESTERS / DIAL THICKNESS GAUGE / FEELER GAUGES / ELECTRONIC COMPARATORS WITH PROBES / DFTMETERS / SURFACE ROUGHNESS TESTERS / DIGITAL= COATING THICKNESS METERS / PROFILE PROJECTORS /.. WE ARE ALSO DEAL IN == DIGITAL TACHOMETERS / =MULTIMETERS! / VIBRATION METERS / MEGERS- INSULATION METERS / =TE! MPRATURE INDICATORS / SOUND-LEVEL METERS / ETC... =AGENCY- FLUKE- RAYTEK.. MECO....LUTRON...KYORITSU....RION... ..................KELIEWS......AND MANY MORE ===AJAY GUJAR ...AJAY ENTERPRISES =08 DALAL CHAMBERS MKTYARD ROAD NEAR NISARG KARYALAYA =MARKETYARD PUNE= 411037.. =TEL= 020 2426 0109. =MOB=09890098941. =EMAIL=AJAY.MITUTOYO@GMAIL.COM =WEB--WWW.GUJARWORLD.COM
Why Instrumentation Air Compressor called as Instrumentation Air compressor?pls dont just tell its trasferring IA to all transmitter,valves.I need exact reason, please......................
what is the PID controller?
can u please tell me the different types of valve uses and wt purposes it is used ~!(controlling the flow other than that which valve should be used in what place)
why pressure 3-15psi is used as industrial standard and what is the reason
2 Answers JAL International, UltraTech,
How many input(Analog and digital) and outputs(Analog and digital) are there in DELTA v DCS Version 7.0?
how pressure reduce through pressure control valve? suppose we have to reduce 20 kg pressure to 10 kg pressure , then what we do ? open the valve or close the valve , initially it is 20 % is upon ( for ur knowledge ).
What is the difference between modbus,fieldbus & profibus
Control valve question what is the meaning of cauge.?what is the use of cauge?
what's the minimum level required of SIL (safety integrity level)to use fire and gas system?
How would i calibrate a new commissioned flow transmitter???
1.what is controller proportional gain 2.what is the controller intergral action time. 3.A proportional plus derivative controller that has a proportional band of 20% and a derivative action time of 0.1 minutes. Construct the shape of the output waveform for the triangular input if the input rises and falls at the rate of 4 units per minute.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)