Answer / binosh
pressure transmitter:
in bench calibration connect a power supply 24v.give a
250ohms as loop resistance.connect a multimeter in
milliamph mode and connect it in series.and put a
communicator across the loop.the transmitters HP&LP sides
should be in open to atmosphere.this condition the
ammeter shows 4ma and the communicator shows LRV .connect a
pressure calibrator to the HP side and LP keep it open to
atm.apply pressure as the range and go on as 25%,50%,75%and
URV.then the ammeter shows 4,8,12,16,20ma
respectivly.incase you are not getting zero,make zero trim.
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / s. kanniyappan
TEMPERATURE TRANSMITTER:
GIVE 24VDC TO THE TRANSMITTER
CONNECT MULTIMETER IN SERIES WITH -VE TO THE TXT
GIVE RESISTANCE INPUT TO THE TRANSMITTER
GIVE LRV VALUE BY ADJUSTING THE DRB
ADJUST ZERO FOR LRV
GIVE URV VALUE BY ADJUSTING THE DRB
ADJUST SPAN FOR URV
GIVE 25%, 50%, 75%, 100% OF URV (RESISTANCE) AND CHECK THE
CORRESPONDING MILLIAMPS OUTPUT
PRESSURE TRANSMITTER:
GIVE 24VDC TO THE TRANSMITTER
CONNECT 250 OHMS IN SERIES WITH -VE TO THE TXT
CONNECT THE HART TO THE TERMINALS OF RESISTANCE
CONNECT THE TRANSMITTER TO THE SOURCE VIA REGULATOR AND MAKE
A T OFF CONNECT TO A MASTER GAUGE
VARY THE PRESSURE BY ADJUSTING THE REGULATOR
MAKE ZERO TRIM FOR ZERO PRESSURE THROUGH HART
ADJUST THE REGULATOR AND CHECK FOR THE LRV VALUE IF NOT
MATCHING ADJUST THE ZERO
DO THE SAME FOR THE URV
GIVE 25%, 50%, 75%, 100% OF URV (PRESSURE) AND CHECK THE
CORRESPONDING MILLIAMPS OUTPUT
DP TYPE TRANSMITTER
LP LINE SHOULD BE LEFT OPEN TO ATMOSPHERE
CONNECT THE HP LINE TO THE SOURCE AND DO THE SAME AS ABOVE
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / rajkumar
Any Txr has input, output, supply. give the simulated input
ie.. mA source or mV or pneumatic and check the o/p. if o/p
doesn't match adjust zero or span . Have details of range of
measurements in hand. In need use them also to get desired
output
Is This Answer Correct ? | 6 Yes | 8 No |
CONTROL VALVE OPERATING IN MANUAL BUT NOT IN MANUAL. WHAT SHOULD BE THE PROBLEM ?
Which standard is used for calibration of Control Valves ?
Tell me the field calibration procedure step by step with diagram of pressure gauge, pressure switch, pressure transmitter, temperature switch, level switch, flow switch, flow transmitter.
what is the process to make control schematic ?
Name four general (not technical) criteria that would you consider important, when deciding upon a particular control valve?
Conversions
Describe all types and levels (4-20mA, 0-10V, mV, pulse, etc.)of analog and digital I/O used in process control application.
How to calculate the flow rate in Vortex flow meter?What is K factor?Can you give me an example calculation to understand the same as better?
is fan is a transducer or inverse transducer?
what is start up vent valve ? why it is used in boiler?
8 Answers ACC, Bhushan Power Steel,
what is full form of NAK?
Why 4-20 amps is being used in instruments? Why cant we use any other range instead of 4-20 amps? Why only 4 amps is taken as lower limit and why 20 amps is taken as the higher limit?