Can we use a 10000 Lph Flow Transmitter in 100 LPH flow line
to get
20mA O/P by adjusting SPAN ?
Answer / carl_ellis
You can do whatever you want to with the span adjustment,
but what do you think the results are going to be?
10000:100 is a 100:1 turndown.
Which flow meter technology that uses an analog adjustable
20mA span has 100:1 turndown?
Which flow meter technology has a HART configurable URV with
a 100:1 turndown?
Flow meter accuracy curves ALWAYS bend exponentially upwards
towards increasing uncertainty as the flow approaches zero
low flow. The lower the flow, the greater uncertainty.
Where do you suppose 100 Lph is on the accuracy curve of a
meter designed for 10000 Lph?
Carl Ellis
Measure First
| Is This Answer Correct ? | 2 Yes | 0 No |
Exothermic reaction./ endothermic reaction
How do you calibration D.P transmitter? ?
what is the difference between(Flame proof/Explosion proof)& Fire proof instruments.Both are same or different & if different in which way because the transmitter which have approved ATEX flame proof enclouser but it use PTPE O ring & PTFE Head Gasket,so its (fire safe/fire proof)????????
To find closed tank level by DP transmitter , how to findout its range.and insomeplace they using range like - 1500 to +1500 mmwc why not 0 to 3000 mmwc. how they spilit they range for minus and plus.and why?
what is compensation in engineering and what is temperature compensation?
Why upper weighing limit of electronics balance is 90% of the total weighing capacity?
What is the electronic transmitter frequency.
How can I make calculation for Install level transmitter (DP) for open tank and cloes tank?
while am calibrating Drager polytron 2IR flame gas detector occured non zero status.how can i get zero status?
suppose, after calibrating a transmitter we fixed it in a process line. At live zero condition the Tx shows 4.5 mA. what should we do to make the Tx show 4 mA? If we adjust zero, will it not affect the calibration?
how to check diode wheather it is working or not by using multimeter?
Why mixer nd grinder Is example of constant torque load not variable torque load ???
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)